Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by MrStohler

  1. MrStohler

    Looking for the 1992 AISC Seismic Provisions

    Thank You, I appreciate the assistance.
  2. MrStohler

    Looking for the 1992 AISC Seismic Provisions

    Thanks for the quick reply. Here's how the reference appears in the AISC-LRFD 2nd Ed. The Dec 2008 edition of Modern Steel Construction indicates the provisions were first published in 1992.
  3. MrStohler

    Looking for the 1992 AISC Seismic Provisions

    I am working on a project where I must evaluate the effects of complying with the current codes relative to an older code (ASCE 7-95). One item of comparison relates to SCBF requirements. ASCE 7-95 refers to the 1992 AISC Seismic Provisions. I cannot find a version of the '92 provisions...
  4. MrStohler

    Austria

    I am interested in information regarding structural design in Austria. Are the Eurocodes the governing codes? Are there local supplements that amend or edit Eurocodes? Are there restrictions regarding who may provide engineering services? What agencies might be able to address these points? What...
  5. MrStohler

    Seismic Design of Foundations in SCBF

    If you are using IBC, it depends on your foundation system. Carefully review Chapter 18 of IBC for the sections relevant to the system you are using. Also consider the loads that will be imposed should the SCBF plastic mechanism is developed (yielding of the braces).
  6. MrStohler

    License Use question

    I would contend that these circumstance are not limited to Illinois. Hawaii also has similar regulations regarding an SE (usually referred to as a Practice Act). Washington, California, Oregon, Utah, and Nevada have limited versions of a Practice Act (there are restrictions on what services a...
  7. MrStohler

    ACI 318-05 Section 8.3.3 factors

    Regarding the approximate factors used to calculate moments and shear listed in ACI 318 Section 8.3.3 (2005 Ed. is in effect for this question) Two factors are listed for positive moment of an end span. One for "Discontinuous end unrestrained" and another for "Discontinuous end integral with...
  8. MrStohler

    SCBF Connection Design

    SCBF connections have several limit states that must be considered. Section 7.1 indicates that the controlling limit state must be ductile. That is, the limit state with the lowest value must be ductile failure mode such as yielding of the plate or "plowing" of the bolts rather than a...
  9. MrStohler

    Stair railing height

    If it is part of a means of egress, a guard at 42" is required in addition to the handrail. (Refer to IBC 2006 Sec 1013).
  10. MrStohler

    Dispositions regarding "responsible charge"

    Thanks southard & rbalex, your quote from FL & CA provide some of the most clear interpretations for responsible charge.
  11. MrStohler

    Dispositions regarding "responsible charge"

    Thank you for the replies. Your interpretations are in line with mine. Specific examples are sought so that independent verification can be applied to similar (but not as clear cut) situations where there are differences of opinion between staff at different levels in the organization. The...
  12. MrStohler

    Dispositions regarding "responsible charge"

    The term "responsible charge" is used by many states to establish who may seal or stamp engineering documents. The definitions offered for the term are usually open a degree of interpretation since it would be difficult to write a rule or regulation for each conceivable situation. Our office...
  13. MrStohler

    India - Is AISC acceptable design option?

    The firm I work for is looking into the potential of designing an industrial structure that would be built in Gujarat India. It would be structural steel construction and the site would fall into Indian Seismic Zone V per the National Building Code of India. During conversations with...
  14. MrStohler

    Seeking a reference for design of steel baseplate with stiffeners (BS)

    I highly recommend Blodgett's "Design of Welded Structures". Although it was written several years ago and refers to the AISC code its methods are still applicable no matter what your jurisdiction. It can be purchased directly from the publisher at a very reasonable cost...
  15. MrStohler

    Unique Connection Help

    Ditto to ajh1. The W27 is very likely to have more than adequate strength BUT the torsional deflection needed to develop that strength could produce unacceptable results. All of the details suggested appear to address the connection of the HSS to the beam flange, but I would suggest that...