I would like to obtain the magetizing impedance characteristic, voltage versus current, of motors and transformers, on site, 4160 V system. I don't think it is so easy, as voltage would need to be varied from below 4160 to above, or use of some frequency methods. Does someone know if this can be...
David, the 0.12 sec I presented was only for the "relay tolerance and setting errors" portion of the coordination time interval (CTI). Additional items for the total CTI, such as breaker opening time, are not in that number, as I am not questioning them. In the reference I provided, total for a...
In Ieee 242-2001, "Recommended practice for protection and Coordination of Industrial and Commercial Power Systems", Table 15-2, a value of 0.12 sec. is given for relay tolerance and setting errors, static relays, coordination time interval, field calibrated relays.
I'm wondering what the true...
AusPowEng, I expect the arc current, generally less than the bolted fault, would then include a reduction in the motor contribution. Stated another way, all contributions are accordingly reduced in going from the bolted to the arc current.
Yes, dpc, it must be that. I see others suggest fuse-fuse as "daylight", and the same for LVCB-LVCB. That seems to settle the fuse total curve as including all tolernaces. So, it must be about CT and relay error. I also now see that some experienced people have a lower interval for relay Inst...
IEEE 242-2001, p605, suggest a coordination interval of 0.12 between fuse and upstream static relay. Others, suggest similar values such as 0.10, for example, http://siemens.siprotec.de/download_neu/applications/SIPROTEC/english/Appl_03_Coordination_of_Overcurrent_Relais_with_Fuses_en.pdf
I...
WDeanN,when you stated that the S/W used by you, allowed specifying synchronous motor contribution over a time period, did you mean that it produces arc flash results at a number of fixed contributions, probably two. Wouldn't actual incident energy be a summation from initial to final, so that a...
That's what I said also: formulae are available. But why choose 1 metre probe depth instead of 100 or 200 mm? If the formulae give the same result, then easier to do 100 mm. And if 1 metre, then why not 2 or 3 m. On what basis would the decision be made as to depth?
Has anyone seen references on the effect of probe depth vs probe spacing using the Wenner 4 point method. It is easy to see statements that spacing to probe depth should be 10 or 20 to 1, and formulae are available when spacing is not much greater than probe depth. However, exact backup is not...
So, when the fault is cleared within 300 ms, the unit comes back to synchronism. It's not too far out at that time that it can't be restored. Is that the objective?
jraef, the box is higher by the physics. In Open, the energy radiates outward, so you mainly get the direct. In the box, you get the direct, but also, reflections off the sides of the box. In IEEE 1584, eqn (4), the constant K1 is the difference in calculating incident energy; higher energy for...
ZogZog, that is what I think also. It's by a Consultant, directed by multi-facility owner. Latest IEEE 1584. I'm an independent reviewer. None of them can form basic sequence networks, but they all have software.