Recent content by MinnesotaSlinger

  1. MinnesotaSlinger

    Steam condensate return piping - cannot continuously slope down

    We are installing a 125 psig steam main through the basement of a building. The amount of ceiling space is quite limited and the run through the building is several hundred feet, so we'll have to trap at every steam main low point where it rises up before sloping to the next low point. My...
  2. MinnesotaSlinger

    IMC Table 403.3.1.1---domestic kitchen exhaust and recirculation

    We're working on a large apartment complex project that will need to comply with 2015 International Mechanical Code. One of our concerns is whether or not we need to exhaust air from each apartment unit's kitchen. In Table 403.3.1.1, 25 CFM constant or 100 CFM intermittent is required for...
  3. MinnesotaSlinger

    Project engineer for power company vs. mechanical engineer for A&E firm

    I've been a mechanical project engineer for two years for a large electrical power supplier, working under contract rather than directly. Most of my work deals with planning, scheduling, estimating, equipment selection, project documentation, design, etc. for small capital projects. (Before...
  4. MinnesotaSlinger

    Power Company Project Engineer vs. A&E Project/Design Engineer---better career path?

    I've been a mechanical project engineer for two years for a large electrical power supplier, working under contract rather than directly. Most of my work deals with planning, scheduling, estimating, equipment selection, project documentation, design, etc. for small capital projects. (Before...
  5. MinnesotaSlinger

    ME career limitations if leaving hospital and plant work for school and church projects

    I'm an ME currently working as a contractor for a major power company leading small capital projects, doing both project management and design work at power plants. I love it, but next year will see a big drop off in mechanical projects in our group, which has me worried that I won't be needed...
  6. MinnesotaSlinger

    Do I need to trap superheated steam drip pot instead of just draining if before opening valve?

    Thanks. Actually, almost all of the steam piping in the plant slopes up. It's all superheated piping throughout the plant. Most all of my prior experience is with saturated steam with steam and condensate flowing in the same direction, that is, downhill with traps at any low point. However...
  7. MinnesotaSlinger

    Do I need a shell-side safety relief on my steam-to-water HX?

    I'm confused as to how to interpret the BPVC Section VIII for my heat exchanger. UG-140 of the code, about overpressure protection by system design, would seem to apply, given that pressure reliefs in the steam distribution system serving my HX are set to relieve at a lower pressure than my...
  8. MinnesotaSlinger

    Do I need to trap superheated steam drip pot instead of just draining if before opening valve?

    Here's a sketch: http://files.engineering.com/getfile.aspx?folder=6eb0992d-fa50-4895-854a-177608d98987&file=4in_line_w_drip_pot.pdf
  9. MinnesotaSlinger

    Do I need to trap superheated steam drip pot instead of just draining if before opening valve?

    I have in the design for my project a 4" line of superheated steam (450-500 F, 80-100 psig) connecting to the top of a 10" header. The line goes up about two feet and elbows horizontally to a manual gate valve. Just beyond the gate valve, I would put in a drip leg with a 1" drain line with...
  10. MinnesotaSlinger

    Steam-to-water HX pressure relief, vacuum breaking, and air removal

    Thanks although I'm not quite sure what you mean by no latent heat. The HX is sized and has materials selected so that the portion near the steam inlet desuperheats the incoming steam and can accommodate the large delta-T. (Ideally, I would have had access to saturated steam, but I don't, so I...
  11. MinnesotaSlinger

    Pipe shield to prevent burns from uninsulated pipe

    On my heat exchanger project, I will have some length of condensate piping that should not be insulated in order to prevent subcooling of condensate before steam trap. However, I want to install a personnel safety shield around the pipe to prevent personnel from burning themselves on very hot...
  12. MinnesotaSlinger

    Steam-to-water HX pressure relief, vacuum breaking, and air removal

    I understand about the superheat, but we don't have a saturated distribution system at the plant. I looked at putting in a desuperheater ahead of the HX (which would have been smaller) and getting a bigger HX sized by the manufacturer for the superheated inlet condition, and I went with the...
  13. MinnesotaSlinger

    Steam-to-water HX pressure relief, vacuum breaking, and air removal

    Thanks, but is there a way to start up a shell-and-tube steam-to-water HX without manual valve operation? The plant has few operators and would want to be able to start water and steam flow to HX remotely without need for manual operation. Can that be done?
  14. MinnesotaSlinger

    Using venturi principle to drive flow through sidestream HX

    I don't have a place to save a sketch online. Basically though, I'd have a 3" schedule 40 pipe with 200 gpm flowing through it. It's downstream of a strainer that would serve both HXs. This line has a tee in it from which 20 gpm will flow out. The other 180 gpm continues on and reduces from...
  15. MinnesotaSlinger

    Using venturi principle to drive flow through sidestream HX

    I am looking to run a small fraction of a flow (say, 10% of 200 gpm) through a heat exchanger. The HX would be selected with calculated venturi D/P in mind. The HX would be for cooling condensate from a steam-to-water HX, which will operate at about 50 psig and therefore have condensate coming...