Yes, if you have a concrete wall above the footing then there is no reason to use the third bar in the top of the footing. Also true if you have horizontal bars in the masonry, but typically, we use horizontal masonry type reinforcing only. I haven't had any issues from a footing since I...
Kootk, The wall above the footing is typically masonry - usually a brick veneer with a 8" block backup. It is not integral with the slab. In the past I have seen engineers place two bars either 3" clear from the bottom or 2" clear from the top - since it is temperature reinforcing it is okay...
A few years ago my engineering firm starting placing longitudinal reinforcing for non-load bearing wall footings in two layers - two bars in the bottom of the footing, and one bar in the top. I am referring to footings that are typically about 24" wide by about 12" thick, and technically are...
Does anyone have advice on selecting a grade for old lumber that was sawmilled before the current grading system? I am looking at engineering a renovation of a 100 year old building, constructed with lumber which is obviously a better grade than #2 SYP. Are there experts who can evaluate the...
The Sinak products look impressive, but they do not seem to be for interior slabs that will receive a floor finish. I know that wet curing is really the best way to go, but still wondering if that is the most commonly specified method for interior slabs. Most of the General Contractors in my...
I noticed that MasterSpec doesn't allow a spray cure compound for floor slabs to receive a floor covering, i.e. a form of wet cure is required. I know that dissipating spray curing compounds sometimes do not dissipate if they are not exposed to light and foot traffic, but they still seem to be...
Definitely use control joints or you will end up with shrinkage cracks in the block. Brick will expand over time, but the cmu will shrink. I have seen many jobs where the control joints were omitted, and the cmu formed shrinkage cracks.
I checked out the FEMA website for suggestions, but their design limits the wall height to 8'. My architect insists on using a 10' high wall, so I do not know if the FEMA design will be helpful. I am also exceeding their maximum horizontal wall dimensions by a few feet. I wanted to find a way...
Thanks WARose. The slowdown distance may be a misnomer, since it came from a physics text where the example was a car crash test. I think it is the deflection, since the unit is in feet or inches. I'll check out Blodgett - that's a great book.
Mike20793, thanks for the Texas Tech...
I am designing a safe room for tornado loads and wondered how other engineers are calculating the force due to 2x4 missile impact. I think the appropriate formula is F = 1/2 x m x V x V / S, where S is the slowdown distance. The appropriate mass seems to be 15 lbs / 32.174 = 0.47 slugs, and...
I'm trying to figure out what has caused this crack pattern in a precast stadium beam. The cracks do not look like tension or shear cracks - maybe they are just shrinkage. The beam is about 3 feet deep and 14" wide. The predominant pattern is 3 or 4 longitudinal, with some random vertical...
Turn down the exterior edges of the slab so that they extend below the frost line is the best way when you are in an area with a relatively shallow frost depth.