Hi to all
I am aware of the fact that high condenser approach is caused due to fouled condenser tubes and/or low water flow in a shell and tube condenser of a water cooled centrifugal chiller. Are there, any other reasons for the high condenser approach?. Would like to get the experts view on...
Thanks willard3 for the answer, but still I would like to know what is the reason for using or specifying the flanged connections instead of other means of joining duct sections. Does this have special application or engineering reason, need opinions of other experts as well...
Thanks
Hi to all
Normally the duct design and construction is divided as low, medium and high pressure system. My question is, as to when and why the flanged duct connection in supply and return ducting is required and recommended, what is the basis of this recommendation? I appreciate and thanks any...
First you need to determine the throttling range required (ie min. to max. temp. required) in your case the air branch pressure from the thermostat is assumed to be 3-13 psi for the the control system.
Next measure the ambient temperature near the sensing element of the thermostat.
Turn the...
Hi to all
I appreciate any responses from our group of experts. Can anybody explain the function of demisters and the labyrinths in the centrifugal chillers.
Thanks in advance
Trigot
Thanks, The chillers in discussion are in 500 to 1000 Tons range, water cooled semi hermetic R-12 centrifugal chillers and are used for comfort air conditioning. These chillers are almost 20 to 25 years old and still working fine without major breakdown or severe problems. Definately as u...
Trigout
As u have pointed out, HOT GAS bypass is in ON mode most of the time for artificially loading of the chiller. If I have not misunderstood your statement, could you please explain, How does a Purge unit eliminate the problem of low oil level during the low load conditions? and do u mean...
Hi everybody
With the scheduled phase out of the CFC based refrigerant(R-12) in the near future, what would be the correct and economical solution for the existing chillers with R-12 refrigerant, is it retrofitting or replacement?.Views and suggestions of the experts in the field are highly...
Thanks imok2 for explaining the issue in a simple way, Does the same principle is used in the hermetic certrifugal chillers to avoid oil transfer between the hermetic motor section and the compressor section. Can anybody else comment as well....
Thanks very much Mr. tombmech for the advice, and as u have rightly pointed out that the OAM Purger deals with entirely a different subject than the question in the thread. However this has started a new discussion, can anybody comment on the real application of these equipments (OAM Purgers) in...
Thanks to all for providing a good information and sharing their experiences, still if anybody else can comment on the problems if any? asociated with using concentric reducer on a Double Suction Split Case (DSSC) vertical Centrifugal pump.
Thanks once again....
Hello to all..
During the low cooling load demand period combined with low ambient conditions, the problem of oil recovery to the oil sumps becomes very serious and sometimes the oli level in the sight glass dispappears, this requires oil charging. Again as the demands increases and also the...
Mr bulkhandling
By vertical pumps, I did not mean the vertical turbine pumps but the split case centrifugal pump mounted vertically, do we need to install the eccentric reducer for this type as well? thanks
Hello to all
I have noticed using eccentric reducer at the pump suction for horizontal centrifugal pumps "Double Suction Split Case" for water pumping in HVAC application. Is this eccentric reducer required for all types of pumps like vertical centrifugal pumps and the end suction centrifugal...
Hi everybody
Cooling tower basin cleaning system are being promoted by many suppliers as an easy and cost effective means of controlling and minimizing the water consumption especially in the areas of water scarcity. These systems have hydro boosters installed in the piping network which is laid...