Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by Marcus

  1. Marcus

    Multiple Resistor Grounding

    hey, no one puts a CB in the neutral grounding circuit of any sized generator. If you did, the generator could become energized to high voltages in the event that a fault occured in the armature winding. resistors and the neutral grounding transformer are sized to create a reactance which will...
  2. Marcus

    Generator field saturation

    hey S, I think you got things mixed up. the dc field in a syn. gen. does not "saturate", however the ac core saturates and this limits the voltage induced in the armature winding by the field. Second, changing excitation (magnetization) levels in a synch. generator changes Var...
  3. Marcus

    is this possible?

    I suggest that you go the the library and read everything you can find written by N. Tesla.
  4. Marcus

    rotor bar cracks

    I am not so sure one can fairly characterize cracked rotor bars in a large industrial motor after 20 years service as "severe" bar cracking" The fact that a large majority of bar cracking was detected at same time, after decades of service, suggests a high cycle fatigue failure...