  1. MagneticFlux

    Motor/VFD Question

    @waross: The drive is a setup for 480 Class (right data column of nameplate)
  2. MagneticFlux

    Motor/VFD Question

    @jreaf: Initially, yes, a Static auto-tune was performed. However, the drive has be reset to factory defaults in preparation for this weekends trial setup per AB Tech Support recommendations.
  3. MagneticFlux

    Motor/VFD Question

    @jreaf: The photo posted of the VFD nameplate is a PowerFLEX 753 http://ab.rockwellautomation.com/Drives/PowerFlex-753
  4. MagneticFlux

    Motor/VFD Question

    b]@jreaf:[/b] One of the AB tech support persons made that statement, I was very clear in my question, "Will the PowerFLEX 753 VFD operate a delta connected motor?", long answer was no. I agree with you and questioned it, and again, was not given a clear answer. I contacted AB support again...
  5. MagneticFlux

    Motor/VFD Question

    @LionelHutz: At ~18Hz, we are drawing less then 1 inch WG on inlet side of duct. It seems to me that there is hardly any load at all. I agree that the VFD should work fine on a delta connected motor. Can you elaborate on motor and VFD/Hz pattern needing to match? Again I agree, the fan...
  6. MagneticFlux

    Motor/VFD Question

    @edison123: Please explain...
  7. MagneticFlux

    Motor/VFD Question

    @waross: The difference in fans are as follows: EXISTING FANS: ~36 inch diameter, ~24 inch width, belt driven, running ~1800+ RPM NEW FAN: ~72 inche diameter, ~19 inch width, direct coupled, 1160 RPM
  8. MagneticFlux

    Motor/VFD Question

    I wish I had good news to report... @iop95: We input your parameter recommendations which yielded marginal results. Was unable to get past 18Hz before reaching FLC. @jreaf: Motor uncoupled from load will run up to base speed (1160RPM) connected delta, current draw ~53 amps (2nd hand...
  9. MagneticFlux

    Motor/VFD Question

    FAN DATA: Fan Diameter: 72 inches Fan Width: 19 inches P Type, Forward Pitch Measurements are the actual fan MOTOR DATA: DRIVE DATA:
  10. MagneticFlux

    Motor/VFD Question

    I have some time scheduled this weekend to visit the site and attempt to resolve this problem. @waross: I will monitor the phase currents and advise. I have asked multiple times for the fan manufacture name and model; no response. I will try and locate this information myself this weekend. The...
  11. MagneticFlux

    Motor/VFD Question

    @waross: Bro, I would NEVER consider someones advice as a waste of time while trying to resolve a problem [bigears]. Regardless of the motors condition (new vs rewound), I have all ready suggested that it be uncoupled and ran. That was done, results; motor ran up to base speed, current about 25%...
  12. MagneticFlux

    Motor/VFD Question

    Thanks all for responding, all good advice. Answers / clarifications to your responses: @jraef: Connection diagram is correct. Yes, motor was not only checked but replaced (had new spare on hand). Distance between drive and motor = ~250', line and load reactors installed within 6' of the...
  13. MagneticFlux

    NEC code requirement

    NEC 230.95 Exception 2: The Ground fault protection provisions of this section SHALL NOT APPLY TO FIRE PUMPS The use of the word 'SHALL' in NEC is mandatory Note that NEC articles regarding services pertaining stand-by/back-up generators should be reviewed and discussed with the AHJ and/or...
  14. MagneticFlux

    Ungrounded 240V System

    Curious, what loads are on the system that would require 240V Delta? Does a grounded system pose a higher risk to personnel safety or the facility? If it {the 240 delta] was installed over 75 years ago, what remains that has not been replaced over the many years? Being able to answering this may...
  15. MagneticFlux

    Maintenance of explosion proof motors by plant personnel.