This problem is being caused by reflected waves and the rapid rise and fall of the pwm waveform. You mentioned load reactors and dv/dt filters on the output of the VFDs...is it both? Do the cables travel through water at all? The readings for voltage you are getting on the output of the VFD -...
Check the output cabling, including opening up the motor termination box to see if there has been anything shorting. I am also curious as to whether you have a solidly grounded system or a high resistance grounded system?
Often Engineers will use a rule of thumb in applying output filters, but it has more to than with just length. It also depends on the system voltage. For example, you should probably always have at least a load reactor on 600V vfd outputs. At 480V, the application of filters on the output of...
Take a look at the Stellar Tech website: http://www.stes.ca/
They have a lot of information there you might find useful under their downloads section.
I consider their product to be the most reliable I have come across, with its real strength lying in the ability of their vfd software and...
Hi krsh,
You do not really need any specific VFD brand for use on pump-jacks, progressive cavity pumps, or electric submersible pumps, the three systems common for oil production.
That being said, many manufacturers, such as ABB, Unico, Yaskawa, Schneider, Vacon, etc..have modified their...
You will need to go closed loop and have a resolver input back to the VFD to control the firing pulses of the drive.
We have done this quite a lot lately and it works very well.
Are you shipping a machine to Europe?
There are three separate issues with CE, the Machine Directive, Low-Voltage Directive, and EMC Directive. Of the three, the Machine Directive is the most complex and is mainly mechanical in nature.
The Low Voltage Directive is fairly straight forward. If...
Another thought: What if we were to mount a large fan blowing on the tank to circulate air on it and create a wind-chill? Would that give us significant gains in cooling and allow for a size of tank that will work?
For example, lets say we were to look at a single VFD with the following characteristics:
losses = 7.9kw
flow rate = minimum= 20L/60s, maximum 40L/60s
nominal flow rate = 25L/60s
pressure drop across drive = 1.96bar @ 40L/60s, 0.43bar @ 20L/min
ambient temperature 30C
how big would the tank...
Hi There,
We would determine the size of the tank based on how large it needs to be to reject 36,230 Btu/hr.
The environment we are working in is an underground mine where water to air heat exchangers seem to not stand up to the dust.
I am wondering if this might be a simpler solution.ie, a...
I am using Liquid Cooled Variable Frequency Drives and am wondering if it would be possible to cool the drives sufficiently using a large stainless steel tank full of water and then a pump to cycle water through the VFDs. The ambient temperature will be a constant 30C. I am not really familiar...