It's absolutely a question of spec compliance, not safety or permanent capacity.
There's a slight effect on the capacity of the cage while it's being tripped to vertical, if the cages are long enough to require multiple rigging points.
I'd have no trouble signing off on it for my projects...
Eh, while this may pan out from an engineering perspective (depending on the method of truss fabrication — many truss connections are more complex and less redundant than a fully welded plate girder), I think you’re sailing toward a fight with the owner’s engineer. I’d start that discussion to...
Looks like a pretty standard column, just happens to have a bunch of eccentric dead load on one side. Design as though 9" wide.
Now detailing -- there's a little bit of detailing attention required here, particularly if the column receives any external load. But that's tomorrow's thread.
Bingo... Whatever permanent and lateral load are transferred to the slab can be resisted by friction.
But because the SOG is often isolated from the remainder of the structural system (to mitigate shrinkage cracking), the majority of the structure's load will first look to be resisted by pile...
Likins suggests (in perhaps this article: https://ascelibrary.org/doi/10.1061/40743%28142%2914) a correlation between factors of safety in the design and the quantity of piles load tested (and type of load test).
From his summary, I believe ASCE 20-96 and IBC were each non-specific when it came...
Yeah, the bolt bending is a killer.
If you can't weld washers, can you oversize the holes even more (or provide a port from the bottom) and inject epoxy or grout to get positive shear engagement at all anchors?
I agree with Rod, you ought to be able to count on some shear transfer through...
Yeah, I'd certainly set two lower limits of 5psf wind or 2% DL. Whether a higher load is appropriate depends a lot on the enclosure (and scale?) of the larger building
Craig beat me to it. Don't discount the stabilizing effect of a heavy load.
And it's hard to get a static friction coefficient less than 0.1, even in wet conditions.