Recent content by kmh1

  1. kmh1

    115 kV Cable Shield Termination

    At a local industrial site they have a set of 30 year old 115 kV single conductor cables terminated using potheads. The shields at the source ends appear to be terminated to ground through a carbon air gap mounted on the cable support structures (see attached photos). Can anyone confirm that the...
  2. kmh1

    Running TECK Cable In Conduit

    In my opinion armoured cable is allowed in conduit as per Rule 12-902 (2) as long as fill ratio and pulling tensions are not exceeded. Multiconductor power cables larger than #1/0 installed according to Diagram B4-4 need to follow the ampacity tables D14 A and B. Rule 4-004 (1)(d) and (2)(d)...
  3. kmh1

    GSU Transformer for 10 MVA Hydropower Unit?

    Thank you. My specific situation is a little different than a standard grid connected power generator in that the generator is a 4160 Volt unit embedded in an industrial distribution system where the system is being upgraded to 13.8 kV and a tie transformer is being considered between the...
  4. kmh1

    GSU Transformer for 10 MVA Hydropower Unit?

    Is a generator step up transformer typically specified for hydroelectric generators in the 10 MVA range or is a standard distribution transformer typically applied? I understand that GSU transformers have different specifications for power flow in the reverse direction for large generators but I...
  5. kmh1

    Substation Ground Fault Currents on Sub-Transmission Lines With No Ground Return Path

    Thank you jghrist, that is along the lines of what I was thinking but I was not able to locate an example or paper regarding this situation.
  6. kmh1

    Substation Ground Fault Currents on Sub-Transmission Lines With No Ground Return Path

    I am struggling on how to address system ground fault currents on load substations connected to 3-wire 44 kV sub-transmission lines with no ground return path (no neutral or overhead ground wire). The utility quotes a zero sequence ground fault current at a point on the line however I am...
  7. kmh1

    Medium Voltage Diesel Generator Frame Cracking

    We believe it to be an alignment issue from installation and/or a soft foot on the generator. The engine/generator sets are CAT supplied in standard winterized enclosures with substantial mounting rails and foundations that meet or exceed the specifications in CAT's mounting guide and there does...
  8. kmh1

    Medium Voltage Diesel Generator Frame Cracking

    CAT done an assessment and haven't come up with an specific explanation either. Apparently they haven't seen this previously. I am thinking mechanical as well but I still haven't ruled out something related to transient oscillations between synchronized machines, possibly due to starting of...
  9. kmh1

    Medium Voltage Diesel Generator Frame Cracking

    Also the units are installed in vendor supplied modular generator enclosures with generator mounting rails and linear spring vibration isolators. They have an 1850 ekw prime rating.
  10. kmh1

    Medium Voltage Diesel Generator Frame Cracking

    The site is in Northern Ontario and presumably the installation work was done by qualified tradesmen per certified installation drawings. The mechanical inspection did not uncover anything obvious including a review of the foundation and alignment procedures. This is installed at surface at a...
  11. kmh1

    Medium Voltage Diesel Generator Frame Cracking

    I have attached a photo of a typical crack. They are 3516C machines and were commissioned in 2010 but I don't have specific information on hours or number of starts. They run an off-grid system so would cycle as needed based on a set priority. The crack appears in the same place on all machines...
  12. kmh1

    Medium Voltage Diesel Generator Frame Cracking

    We are working on a situation at a remote mine site where four 4160 Volt, 2 MW Caterpillar diesel generators are operated in parallel in an off-grid configuration to provide power for the site. Over the span of many months, several of the generators have been experiencing cracking of the stator...
  13. kmh1

    Solar PV Array Grounding

    Thank you, we are presently modeling the site using SES software. I was curious to see if installing a buried ground conductor around each array support was commonplace or just around the overall perimeter of the site. The SES software should uncover any hazards but the extra buried copper...
  14. kmh1

    Solar PV Array Grounding

    I am working on completing a ground potential rise and grounding study for a large 10 MW ground mounted PV installation. The site will be interconnected to the utility grid via a 44/12.5kV substation with the substation ground interconnected with the PV module grounding system. The 44kV system...
  15. kmh1

    7.2 kV Distribution Shunt Reactors

    After further investigation it appears that several factors were at play here. Firstly, the reactors only appear to have been designed to rated current at nominal voltage, as there is no maximum operating current or voltage listed on the nameplate. Secondly, the units are 115 deg C rise units...