  1. KJvR

    MV Switchgear rating and IEC909

    (a) Ik (steady state short circuit current) or 30 cycle Ib (symm break current) for short time current rating of the breaker and switchboard - Thermal (b) Ib (3 or 5 (for older MV breakers) cycle symm break current) should be use for the breaker's fault current breaking capability (c) ip...
  2. KJvR

    Bus admittance matrix vs hand calc

    Yes, for all three phase balanced faults. Your bus admitance matrix for unbalance faults will have to be compiled from an equivalent sequence component circuit or using Modal domain to decouple the impedances.
  3. KJvR

    How to find zero sequence impedances for 3winding transformers

    Thanks chuky for your valuable post. Do you have a reference to that info as the Yyd transformer zero sequence impedance is different from the typical values I have used in the past. I did recieved actual values on a small Yyd Tx once from a manufacturer and the zero sequence imp was about 1.3...
  4. KJvR

    How to find zero sequence impedances for 3winding transformers

    You will have to ask the manufacturer for the exact impedance values. For preliminary calcs use X(0)/X(1)=1. This is normally an adequate approximation for all YNd (0.8-1.0), Dyn (0.9) and YNyn transformers. Different values should be use for Yzn (0.1-0.15) and YNyn0d (1.5-3.2) transformers. I...
  5. KJvR

    3 winding transformers

    I am more familiar with the Australian Standards (AS3851 - Calc 3 phase short circuit currents) but it is based on the IEC 60909. AS 3851 (and I assume IEC 60909) provides a very simple guide on how to represent a three winding transformer using three two winding transformers in either a star...
  6. KJvR

    http://capps.wsu.edu/conferences/wprc/Brochure.pdf

    Hi David, it does look very interesting. Would you mind elaborate a bit on your research or is there an abstract available on the Web?
  7. KJvR

    ATP BCTRAM model transformer

    Hi Arango, I have never try to simulate inrush current using ATP but can give you some advise in entering saturation data into your model. As far as I know, you will not be able to use BCTRAN to simulate saturation and hysteresis. I would appreciate it if you can let us know if you do find a...
  8. KJvR

    Effect of conduit size on cable derating factor

    cgrondzinski, thanks for showing me the difference in resistivity and resistance. Hopefully I will not mixed it up in future. I aggree with dpc that the influence of duct size on the overall ampacity is very small and the duct size is a function of the cable diameter and not a way to increase...
  9. KJvR

    Effect of conduit size on cable derating factor

    Your cable rating will increase (because thermal resistivity will reduce) with the increase in duct diameter. The influence are: (a) Thermal Resistivity through cable air from cable surface to duct inside surface - mostly (but not totally) independant of duct size (b) Thermal Resistivity...
  10. KJvR

    Surge Arrester in Parrallel

    swgrmfg, you are correct - I have refered to a series and shunt gapped MOSAs as I thought they might be the worst case.
  11. KJvR

    Load

    It sounds as if you are on one of the gold/platinum mines in S.A. - most of the older mines used ONAN transformers. If so, you can then possibly uprate the transformer to ONAF and get a few extra MVA. Also, the main incoming transformers normally have on-line tap changers that will easilly...
  12. KJvR

    Surge Arrester in Parrallel

    I aggree it is an interesting question. My knowledge is limited to modeling and some theory. The first MOSA that have a spakover of the gap will cause a drop in the voltage that can cause a reduction in the current of the second MOSA to below the spark-over point(this current is well within...
  13. KJvR

    Generator Steady State Fault Current

    Hi Mineguy, the particular switchgear that we will be using specify various ceilling heights for various fault currents for Internal Arcing Current Certification - the busbars is very high in comparrison to other MV switchgear. IEC 62271-200 or IEEE 37.20.7-2001 provides more detail for IAC...
  14. KJvR

    Generator Steady State Fault Current

    It is a ABB - UNITROL-F AVR. The purpose of the calculations is for the substation ceiling hight design. The manufacturer provide certain minimum ceiling hights for specific fault currents (busbar arcing faults) and fault duration. I want to calculate the I2t during the first 0.5 sec or 1 sec...
  15. KJvR

    Generator Steady State Fault Current

    This might be a dump question but I get lost every time I have to do something on a generator. I must calculate the steady state fault current (energy of fault) of a bus being fed by both the utility and two small 13 MW MV generators. I have the AVR settings. It states: "Current Limiter...