Recent content by Kalikot

  1. Kalikot

    Smoke removal in multi-storey building

    The project is on the Middle east. I read on the IMC that it is not required if the window is openable otherwise you should design it by 10 ACH.
  2. Kalikot

    Smoke removal in multi-storey building

    What code does it pertain? What is the requirement in term of designing the extract airflow requirement? Does the existing extract fan suitable enough? Is this option only?
  3. Kalikot

    Ventilation standard ASHRAE 62

    Anybody has an electronic copy of the said standard?
  4. Kalikot

    Laundry equipment heat gains

    The project is a hotel laundry. Our scheme is to feed by air handling unit.I think the most of the loads will come from fresh air from drier, press machines and washing machines. I saw many laundries that are poorly airconditioned due to a/c equipment sizing.
  5. Kalikot

    Laundry equipment heat gains

    How can I calculate the heat gains (airconditioning load) of the laundry equipment? KW = steam rate X enthalpy x factor? Where can I get equipment factor?
  6. Kalikot

    Variable Refrigeration Airconditioning

    Yes, there is a recommemded max. length and pipe diameter written on the catalog however I am aware if they are counting the losses in fittings especially elbows.
  7. Kalikot

    Variable Refrigeration Airconditioning

    What is the method for pipe sizing of vrf a/c system? Is the old/traditional method of refrigeration pipe sizing apply? Is the y-branch is a special fitting?
  8. Kalikot

    High Voltage Room Airconditioning

    As what I understand on the NEC 110.26(F)(1), the acu unit is prohibited to be installed above any electrical equiptment but does not prohibited to be installed within the room. Please clarify?
  9. Kalikot

    High Voltage Room Airconditioning

    Is there any rules and regulation regarding the installation of air conditioning unit which feed by chilled water system? I am aware for possible water drip off and water leakage on the piping. If so is it applied also to tranformer room and low voltage room?
  10. Kalikot

    Expansion Tank Location

    Thanks for the advice unluckily I don't have that reading material. Anybody has a copy of this article even a condensed type?
  11. Kalikot

    Expansion Tank Location

    The pump is located at the ground. The typical max. working pressure of the expansion tank is 150 psig considering the static pressure elevation which at 140 psig, is it safe to locate it on the ground with the pump.
  12. Kalikot

    Expansion Tank Location

    Where is the best location of expansion tank for chilled water system if the building is multi story around 100 meters high?
  13. Kalikot

    chw/hw pressurization pump

    Joesteam pick up my question, normally city water pressure are common use but nowadays designer are installing permanent pressurisation pump because of non stable pressure of city water and to avoid possible mixing of chemical treated water to city water.
  14. Kalikot

    chw/hw pressurization pump

    Sorry If I dont make it clear, so pressurisation pump is one which makes filling and pressuring up the system. The AHU means Air Handling Unit - 1 no.
  15. Kalikot

    chw/hw pressurization pump

    I am involved once on the design and selection of chw/hw pressurization pump, I just used to calculate the flowrate by assuming that 1 AHU is under flushing condition. Is there any standard procedure to calculate the flowrate of pressurization pump?