  1. jwerthman

    Multilin SR 489 relay

    I agree that you need to check with GE. You can probably upgrade the firmware for the older relay so that both relays are the same. Firmware upgrades are usually quite easy with the GE/Multilin devices.
  2. jwerthman

    West. MOR-A

    I looked on the Cutler-Hammer web site and there is a lot of info about the MOR relays. I'm not sure it's what you need, though. Go to the search engine on the C-H site and search for MOR. Good luck.
  3. jwerthman

    Pole slip protection/ calculations

    Download GER-3179 and GER-3180 from the publications section of the General Electric web site: www.geindustrial.com
  4. jwerthman

    cable impedance

    Why would you use a 600 volt base to calculate per unit for 69kV cable? Is the cable actually connected to a 600 volt system? If not, I think you are using the wrong base voltage for that cable. Remember that the base MVA stays the same, but base voltages change across transformers.
  5. jwerthman

    Parallel cable impedance

    Do your math again. I used R=2 and X=2 and came up with the parallel combination of Z=1 +j1 which is correct. Be careful of all the j^2 terms in the equation - don't forget that j^2 is -1.
  6. jwerthman

    Odd Potential Transformer Readings

    It's not surprising that you are getting those voltages to ground with the connection that you have to the meter. With no reference connection to ground, the entire metering system is floating with respect to ground and the line-to-ground reading will be all over the map, as you are seeing. An...
  7. jwerthman

    Pony Motor

    I have seen both approaches used successfully. The tandem 50% capacity motors has some appeal particularly if there are times when only half the power is required. It can also provide some redundancy at reduced capacity, which may or may not be worthwhile in a sawmill application. With either...
  8. jwerthman

    Rotor Earth Fault Protection

    Call Chuck Mozina at Beckwith Electric. The standard 3425 relay is only rated for 600 volts DC, but Beckwith does a lot of custom designs and the price is usually not unreasonable. I'm sure they could come up with a design for 1200 volts.
  9. jwerthman

    Drive Isolation Transformers

    For a single drive, I don't think it really matters. The only real effect of either the delta-delta or the delta-wye isolation transformer is to provide additional source impedance. The delta-wye connection would provide some shunting of triplen harmonics except that the neutral is normally...
  10. jwerthman

    Transformer Connections

    The Yyn connection will phase out OK with the delta-delta connection that you have now, but it will not eliminate the grounding transformer unless the Yyn transformer includes a delta tertiary winding sized to provide an effective ground and to carry the continuous neutral unbalance current.
  11. jwerthman

    EARTH FAULT RELAY OPERATION FOR JUMPER OPENING

    jghrist - If the 11-0.44kV transformers are the only load on the 11kV system, then I agree with your comment. I assumed that the 11kV system was a typical 4-wire distribution system that would have single-line-to-neutral loads and a few delta-wye transformers that the original post mentioned...
  12. jwerthman

    EARTH FAULT RELAY OPERATION FOR JUMPER OPENING

    There are two possible reasons that the 66kV earth fault relay operated under the conditions that you have described. 1. With a YnYn connection on the 66-11 kV transformer, the 11kV system would also see only two energized phases when one of the 66kV phases is open. If there are...
  13. jwerthman

    %Z0 vs %Z

    The zero sequence impedance of a three-legged core form transformer will be 85-90 percent of the positive sequence impedance as stated previously. For five-legged core form or shell form or any configuration that has a complete magnetic circuit through the core for zero sequence flux (i.e. no...
  14. jwerthman

    Which bulb lights first?

    Very good DanDel. You get a star for that!
  15. jwerthman

    Generator neutral grounding - Reactance type

    Reactance grounding is commonly used where the generator must supply unbalanced line-to-neutral load. Resistance grounding cannot be used in this application because the resistor losses would be prohibitive and the resistor would run quite hot due to the continuous neutral current.