    Generator Insulation Testing

    I am interested in three tests used on the insulation systems; both stator and rotor windings. These test are the Poalrization Index, Dielectric Discharge and Step Voltage. I have used PI testing on my generators forever and am considering adding both Dielectric Discharge and Step Voltage to...
  2. jplinn

    Motor Protection

    What is the typical setpoint and basis for unbalance protection on an induction motor. Specifically, magnitude differences between the 3 phase currents, negative sequence current and negative sequence voltage. Background - Induction generator when fully loaded trips off due to current...
  3. jplinn

    How to find the inital formula behind engineering test data ?

    Fit your data with TableCcurve 2D www.systat.com/products/TableCurve2D It will give you the best fit, the statics for the fit, residuals, prediction interals and fit intervals with a select confidence level. Then put the formula into a spread sheet
  4. jplinn

    Rotor Interturn Fault

    Did you check the Diodes and fuses to insure the the bridge is working correctly? I believe on a rotating exciter you use an indirect measurtement for field current. A blown diode or open fuse may be limiting the field current. If the bridge is working correctly. perfrom an open circuit...
  5. jplinn

    gaining and loosing engineering specialties

    Work in the power industry (Mechanical and Electrical) will be up in future. It is estimated that the retirement rate will be 50% in the next 5 to 10 years. Several utilities expect to lose 70% in that time frame. At my company I am already seeing the rate of retirements grow. I also am...
  6. jplinn

    Generator Impedance and Stator rewind

    motorspert You sent me back to my books (and associates) to review the calculation of machine impedances and time constants (at Design). Here is what I condensed from that review. Reactance and time constants will be the same for a machine with the same parallel to coil turn ratio. A change...
  7. jplinn

    Generator Impedance and Stator rewind

    Generator reactances and time constants are a function of the stator geometry. Rewinding the generator with a different winding configuration will not change the reactance of the machine. Increased copper sizes will decrease the resistance.
  8. jplinn

    Recommendations for MS EE program

    At least with my company (Electric Utility)we are hiring new EE graduates (or graduates with 1 to 2 years of experience. Then putting them with seasoned engineers to develop there power expertise. We do no not look overseas for new grads. Due to the nature of utilities being part of local...
  9. jplinn

    Recommendations for MS EE program

    I am in the power industry (utility). One thing interesting about this industry is the retirement issue. 40% to 50% of this industries employees are eligible for retirement within the next 5 years. Management is figuring this out and is getting concerned. In addition, a ton of new power...
  10. jplinn

    Wrong generator synchronization ?

    You should inspect your damper bars. During an out of syncronization large currents can flow in the damper bars. I have inspected several units that have been closed in out of synch and on both I found burning on the damper bars. In addition, you should check the slip rings. During a out of...
  11. jplinn

    Electrical Insulated Hydrogen Seal

    Two flanges bolt together with an electrical insulating gasket between them. A bolt from the outside of the 'vessel' hold the inner piece to the outer piece. The bolt hole is electrical insulated by a washer and nonconducting tube. The bolt head is at air atmophere pressure. The insulated...
  12. jplinn

    Synchronous Motors

    When evaluating your machine for a generator you have to assume that a load rejection happens and the wicket gates do not close, hence the unit goes to the runaway speed. Your generator must survive this speed the specific amount time necessary to shut the unit by additional means. Example...
  13. jplinn

    Synchronous Motors

    You can use a synchronous motor as a generator. However, for hydro application over speed becomes a critical concern. Upon a load rejection the turbine generator can easily reach speeds of 2 times normal running speed. In the event of load rejection and failure of the wicket gates to close the...
  14. jplinn

    Generator Vibration

    We had a similar problem at one of our combustion turbine generators. The problem was a result of non-uniform coil expansion under the retaining ring. As the coils grew out the imbalance became worse and coil growth was a function of field current. Based on your description I would 'guess'...
  15. jplinn

    13.8 kV GENERATOR-INSULATION EVALUATION.

    I realize this is too late to be of use, but I have been in the field since May working on our generators. If the situation happens again maybe this will be useful. The same situation has occurred several times in the last few years on the generators I manage. On all of the occasions I...