Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by joozu6

  1. joozu6

    High-Rise Voltage Drop Solutions

    Good point Bill. It would be mostly resistive load. I'm curious how far (how tall of a building) increased cable size would get you before it is no longer cost effective, versus installing additional transformers on multiple floors. Also, could you have the customer install step-transformers...
  2. joozu6

    High-Rise Voltage Drop Solutions

    These are helpful. Thanks. Has anyone heard of using capacitors to raise voltages in this scenario? I'm thinking of leveraging AMI meter data to monitor voltage, and using controlled capacitors on the secondary voltage side to raise secondary voltage as needed when the loads are high. Then we...
  3. joozu6

    High-Rise Voltage Drop Solutions

    Our city skyline is getting taller. So much so that the new taller high-rises are limited by voltage drop. We are having this issue on our Network system, where we typically service customers from the ground floor with either 480V or 208V. We considered running primary up the building and...
  4. joozu6

    Transformer Connection 3PH Open Delta 480V w, 2-Bushing Xfmrs

    We're trying to phase out the open delta banks, so when an open-delta transformer fails the linemen are replacing them with 480V wye banks and not running the neutral. However, we're told this is a safety issue and could burn up the customers' equipment.
  5. joozu6

    Transformer Connection 3PH Open Delta 480V w, 2-Bushing Xfmrs

    Thanks. I thought so. If a customer is on a 480V open delta, is there any reason not to give them a 277/480V wye service and just run the 3-480V legs?
  6. joozu6

    Transformer Connection 3PH Open Delta 480V w, 2-Bushing Xfmrs

    We have some 2-bushing 277/480V overhead transformers in stock and would like to use them to install a 480V open delta bank (versus using 3-bushing transformers that have a center tap, which we don't have in stock). I'm not a transformer connection expert, but I'm thinking I can delta-connect...
  7. joozu6

    Transformer (Overhead 10-167kVA) Ground Wire Size

    My utility started using a #2 Stranded Copper for their loop ground on overhead distribution transformers (versus #6 solid copper previously). I can't figure out the reasoning to this. For a 167kVA 120V transformer the fault current is max 57,300 amps. With this size fault current the...
  8. joozu6

    Ampacity Ratings of Urd Power Cable

    No. They are all XLPE. Thanks.
  9. joozu6

    Ampacity Ratings of Urd Power Cable

    Some were more specific than others, but for most of them it is one cable per duct. No filling was mentioned.
  10. joozu6

    Ampacity Ratings of Urd Power Cable

    Correction, Rated at continuous current @ 90 DegF
  11. joozu6

    Ampacity Ratings of Urd Power Cable

    In trying to determing the ratings of underground cable for my company I determined that the manufacturers vary widely in their ratings, i.e., for 25kV 4/0 Copper 1/3 neutral 260 Mil insulated cable buried in ducts: Southwire = 287 Amps, King Wire = 320 Amps, and Perreli = 314 Amps. The ratings...
  12. joozu6

    Installing 1 Cable per Metal Conduit - Problem?

    Thanks resqcapt. Seems like the NEC is supporting putting all phases in one conduit if using metal conduit. I'm thinking of going to a high scheduled pvc, though, instead of putting all the phases in one conduit. That way if we fault a phase we won't loose all three.
  13. joozu6

    Installing 1 Cable per Metal Conduit - Problem?

    We use a stranded concentric neutral that comes on the parameters of the urd cable. Sounds logical in theory, but I still haven't found any documentation on the subject and haven't experienced it on any of our metal conduit.
  14. joozu6

    Installing 1 Cable per Metal Conduit - Problem?

    That helps jghrist. Thanks. Would a shielded cable help?