Thank you all for your inputs !
I looked at the cost of procurement and installation for a MV 100km submarine cable, and we are in the range of $40,000,000 USD! and it would be technically challenging, with reactive compensation issues, steady-state voltage rise, transients, charging current...
Hi all,
do you have any suggestion for the power supply of an unmanned offshore platform:
distance from shore: 100km
load: 50kw
How about using DC with a rectifer/inverter combination?
Thanks !
I'm not familiar with the control system at all.
I will certainly point out that fact, that the start frequency is way too high.
From a power quality stand point, everything looks Ok.
I will ask them to modify the system and see if fuse still operates and also monitor contactor wear.
JL
jraef,
in fact, the recorded data are the max & min value for the entire minute interval.
For each 1 minute interval max & min values for the current, during this minute, are recorded.
JL
See attached file:
after 2008-10-20 @ 04:42:33, the current in phase A goes up to 75A when compressor attempt to start.
Question is: is it normal to draw more current on two other phases when attempting to start a motor with a blown fuse on one phase?
Thx
Hi all,
we've been asked to investigate fuse tripping on a compressor starter:
Compressor nameplate:
RLA: 16.8A
LRA: 84 A
Fuse:
Low-Peak
class CC
current limiting
LP-CC-30 (30A)
Contactor:
Siemens
42BF35AJ
FLA:30 A
LRA:120 A
15HP 3ph
First thing we did is hook up a power recorder to the...
What would be the typical impedance of a voltage regulator?
Exemple: 400A , 14.4 kV ,±10%, (576 kVA)
Since it is an auto-transformer, I expect the impedance to be lower than a regular transformer.
Any typical impedance?
JL
apowerengr:
the plant is in connecticut, the rental of 400 amp vregs could be a good option.
any information about companies that could sell/rent this kind of equipement? i'm in discussion with local utilities about this, but I would like to have a couple of options.
Thank you.
itsmoked:
It is a steam powered generator, the steam comes from a gas boiler that will be replaced by three bark boilers. The steam generated by this gas boiler is also used in the process.
During the time of the project (3 years), the steam required by the process will be supplied by some...
That is true davidbeach,
but since it is a 20MVA generator supplying only about 6 MW, there is no benefits to run it at 1.0 pf.
I think it will all come down to pricing...
Capacitor banks needs maintenance, protection study, harmonic study.. etc.
Voltage regulator tranformer might be more...
Hi all,
here's the situation; a 20MVA generator will be shutdown for 3 years at a papermill. This generator was providing all power factor correction needed by the plant. And about half of the load. (Total load is 12MW, 5.7MVar)
When the generator is down, pf at service entrance drops down to...
Hi all,
we are working on design and construction of ground grids for a wind farm.
For each 1.5 MW generator (80 total), GE is specifying ground grid resistance of 2 to 10 ohms.
With the data we have:
-ground resistivity : 500 to 1000 ohms, average
-projected ground grid area: 285 m^2, (about...
I'm talking about reactance.
We need it to install on the high side of a step up transformer (600/25000Y), for a 2MW hydro plant.
The goal is to reduce the phase-ground fault current and to stay solidly grounded at the same time. Utility requires that.
I will communicate with Trench, as the...