I have specified a G60 coating for cold formed steel framing at a wastewater treatment plant. The contractor has submitted product data for material with a "CP60 coating" This designation apparently covers galvanized (G60), galvanneal (A60), galvalume (AZ50), and galfan (GF30). My spec...
Good morning. I posted this on the Materials Engineering forum and didn't get many bites. I'm hoping it's O.K. to try to direct traffic to it from here.
http://www.eng-tips.com/viewthread.cfm?qid=455116
JKW
Say we're fastening a nominal 2x member to another nominal 2x member with lag screws.
2015 NDS 12.1.4.6: "The minimum length of lag screw penetration, pmin, not including the length of the tapered tip, E, of the lag screw into the main member of single shear connections ... shall be 4D."
If a...
The frame is used to test safety harnesses.
The standard specifies the minimum natural frequency of the drop test structure. Don't know that I can buy into it meaning anything other than the structure....
Thanks for your input.
JKW
The referenced requirement from the standard is quoted in the 4th post of this thread.
"I've always taken the simplification of 18/sqrt(9.81)as shown here for a uniformly distributed mass & stiffness case:-"
Where did the 9.81 come from? Did you mean 18/sqrt(delta)?
The first two forms...
The impact load is 200 to 300 pounds. The 200 Hz requirement is from the ANSI Z359.7 standard referenced above, although I do not know what that requirement is based on.
Thanks for your responses guys.
SocklessJ, you indicate that my analysis is based on load, not mass. But all 3 of the derivations I posted use the basic equation of f=[1/(2 x pi)] x (k/m)^0.5 where m=W/g. Except for the discrepancy between the 0.18 and 0.16, this is also consistent with what...
I had modeled the frame in an analysis program with the following results:
Beam Deflection: Model = 0.00048"
Hand Calc = 0.000394" (simple beam = 5wL^4/384EI)
The frame analysis program includes shear deformation which I have calculated to be 0.000094"
Beam Deflection: Model =...
patswfc:
We have discussed the axial shortening condition in our office. I agree the deformation is already in place, especially since it is an existing frame. But the question to us then becomes do (can) we also ignore the beam self-weight deflection which has also already occurred. The...
ANSI Z359.7 "Qualification and Verification Testing of Fall Protection Products", Section 4.1.1:
"The required minimum natural frequency of the drop test structure shall be 200 Hz when measured along the vertical axis through the point of the test anchorage or anchorage connector to which the...
I have attached a sketch and calculations for a simple frame which will have a very small impact load applied downward at the mid-span of the beam. The required minimum natural frequency of the structure measured along the vertical axis at the mid-span of the beam is 200 Hz. From the attached...
ASCE 7 defines hi as the height to Level i, with "i" being the buiding level and i=1 being the first level above the base. The attached file shows three typical building sections (I hope I attached it correctly).