I don't work in IEC standards, but I will say that the drives do not contribute to a fault in anything like the same way that the motor directly would.
The drives may even be able to limit 1/2 currents. I know this is true of modern solar inverters.
Definitely incorporate Waross's discussion...
I'm agreeing with Stevenal on all points made:
Many modern multiprocessor relays will compensate for the phase shift automaticaly. If your relay does not do this, you will have to compensate for the phase shift by CT secondary connection.
Also agree that hiring a protection engineer would...
Rafiq,
I definitely understand limiting your time investment.
My question is really about what equipment can but used for "Modified Differential Ground Fault (MDGF) / Multi-Source Ground Fault (MSGF)" in 480/277 systems.
It appears that the answer is equipment listed to UL 1053. The best I...
Rafiq,
Thanks for the reply. 4 Pole ATS's would certainly solve the problem.
Three factors have us leaning away 4 pole ATSs.
1. One of the 3 pole ATS's is integrally installed into the Main SWBD. Even if we could find a 4 pole unit to fit into the enclosure, the needed outage time is far...
Try pasting from your application into a text editor first. Notepad for example. Then copy from notepad and paste to excel.
Or save the notepad doc as yourfilename.csv and open it with excel.
Greetings All,
I'm consulting on an 480V 3ph 4W ~1.5 MVA system that powers a building and small data center on a university campus in the U.S.
There are three power sources to this system, each with an independent bonding jumper. Each on a different SWBD. The system wasn't designed that...
Jraef,
I'd never considered it before, but the method you describe as "Sensing the back EMF" makes a lot of sense.
I can't begin to understand, however, how it would come to be know as ""Sensing the back EMF".
Anyone have any ideas about this?
JBinCA
dpc,
Thanks again for the reply. I have not gotten accurate data on the GFD settings yet. I have been assuming that increasing the delay band is the right way to correct the problem.
Regards,
JB
Davidbeach - Thanks for the response. Are the CTs in ICCBs not rated similar to protection class CTs? I can't remember reading it specifically, but I would think that they would be rated such that saturation would not occur until after 20 pu current.
As to the general question, I understand...
If the device is one of motor operators that mount on the front of MCCBs (as DPC thinks), it's worth pointing out that while the closing evolution is slow, the actualy closing of the contacts is not. The handle is moved slowly, but the contacts close rapidly once the handle gets to the right...
Greetings All,
I'd like to solicit opinions on the following question - Should there be any significant zero sequence (ground) current during the energization of a XFMR?
The event which gives rise to my question is a ground fault trip that happened when the XFMR was energized with no...