Recent content by instrument1717

  1. instrument1717

    Frozen Pipe idea

    Necessary protections must be at welding machine primary , and start with minimum current. without protections inadequate operation may damage the machine.
  2. instrument1717

    Frozen Pipe idea

    Low voltage high current injection units will help( or old welding machine ). For Metal Pipes Use current from welding machine ( without Grounding ) , Connect between flange to flange , the line and the Solid ice will be heated fast .A little current will leak to earth , but the purpose shall...
  3. instrument1717

    Weight required to relief pressure

    reena1957 is Correct , The weight (force ) required for 0.6kg/cm2G with inlet Dia of 0.4mt shall be calculated as follows. Weight(force) = Set pressure (in Kg/cm2G) * inlet area of the valve (in Cm2) In your case it is 0.6 kg/cm2G * 1256 cm2 = 753.6 kgf. The Lever system should excert...
  4. instrument1717

    Deaerator Level Measurement

    if Going for changing the type of level measuremnt, The best choice is guided wave .The displacer instrument also will subject to the pressure surges to some extend .
  5. instrument1717

    I want to get more knowledge about PLC

    INFO : Siemence STEP7 programm has a built in PLC simulator to test the programm . A bit Preliminery knowledge is essential,But is usefull for learners who dont have PLC acces.
  6. instrument1717

    VSD Question

    davidbeach, I can agree with you only if the protection programms are put in cyclic scan ...In that case Typical scan time lies between 100ms to 500 ms. But It can perform very fast protection functions (while online) with an inturrupt programm which temporarily hault cyclic program...
  7. instrument1717

    VSD Question

    The Primary Level of protection must be within The drive . (Protections with External /other units (like PLC )are not an alternative for this .) Yet ,One can have addtional secondary protections in external systems ( Like PLC ). In the event of primary detection failure the secondary will...
  8. instrument1717

    Magneticlly lached contactors

    Suggession : Never Replace a DC coil ( or where DC coil is to be put ) with an AC coil of same voltage rating , It may malfunction /burn.
  9. instrument1717

    Burning contactors

    My Opininon : If possible Try with Better Contactors of different make ( Fast switching with bettter rating specs ).
  10. instrument1717

    neutral cable burnst on asincronous generator

    If it is a single unit of Power source I Suspect you had bad connection ,which burned by severe ground fault in system. I my opinion (opinion only ) faults while in a synchronised system may result the same situation if the weakest point( Bad Connection ) was neutral- Ground connection and...
  11. instrument1717

    magnetrol displacer control valves

    Hope You have a displacer type level instrument ,a level controller at DCS for level control and a control valve on line. It can be a problem at low ampient Temperature ( It happenes very rarely ) 1. with electronics circutry of level controller or 2. with electronic circuite of i/p...