Look at NEC 250.142 (A) which allows the grounded conductor (neutral) to serve as the equipment grounding conductor on the supply side of the service disconnecting means.
The generator was evidently removed by the previous tenant. Is it a reasonable assumption that there exists the functional equivalent of a service entrance rated transfer switch?
Thanks for all the help,
Dave
Thanks all. I have attached a better photo of the nameplate.http://files.engineering.com/getfile.aspx?folder=63e8c12b-29a5-42ab-be3d-28bdde8477be&file=nameplate.JPG
Can one of you more international gents let me know what this device is? I think it is a generator transfer switch.
A USA associate is looking at properties and needs some advice as to electrical infrastructure.
Thanks,
HDP
NEC Article 240.21C2 permits these secondary conductors to be run 10' without additional protection, providing the conditions of this article are all met.
I believe Bill's post is on the money. I worked for years for a mid-southern utility. One particularly bad storm involved a heavy freezing rain. It was a 20 year event. We started patrolling, looking for open cutouts. We had to backtrack when a veteran explained that the fuse barrels might...
I have been involved in a couple of situations where a single-phasing event during a storm was interpreted as a "surge" issue. In both cases, the contractor control power was derived inside the customer facility from a 480V-208Y120V transformer. The damage was caused by the reduced voltage on...