  1. hdp

    Oil Filled Cables

    Potheads are seldom oil filled in my area (USA). There are filling compounds with varying properties, everything from petrolatum to Ozite.
  2. hdp

    System Grounding

    Look at NEC 250.142 (A) which allows the grounded conductor (neutral) to serve as the equipment grounding conductor on the supply side of the service disconnecting means.
  3. hdp

    Amsterdam Electrical Device

    The generator was evidently removed by the previous tenant. Is it a reasonable assumption that there exists the functional equivalent of a service entrance rated transfer switch? Thanks for all the help, Dave
  4. hdp

    Amsterdam Electrical Device

    Thanks all. I have attached a better photo of the nameplate.http://files.engineering.com/getfile.aspx?folder=63e8c12b-29a5-42ab-be3d-28bdde8477be&file=nameplate.JPG
  5. hdp

    Amsterdam Electrical Device

    I'd use Google to find how to say "Thank You" in Swedish, but I fear what that translation might say! Dave
  6. hdp

    Amsterdam Electrical Device

    Thanks, Gunnar! I knew your translation would be far superior to Google. Google gave me "emergency generator"! Best to you, HDP
  7. hdp

    Amsterdam Electrical Device

    Can one of you more international gents let me know what this device is? I think it is a generator transfer switch. A USA associate is looking at properties and needs some advice as to electrical infrastructure. Thanks, HDP
  8. hdp

    Over Current Protection on The Secondary ?

    NEC Article 240.21C2 permits these secondary conductors to be run 10' without additional protection, providing the conditions of this article are all met.
  9. hdp

    Power out at Super Bowl

    This was run in the Chicago tribune. http://my.chicagotribune.com/#section/-1/article/p2p-74345124/
  10. hdp

    Curious Cutout Fuse

    I believe Bill's post is on the money. I worked for years for a mid-southern utility. One particularly bad storm involved a heavy freezing rain. It was a 20 year event. We started patrolling, looking for open cutouts. We had to backtrack when a veteran explained that the fuse barrels might...
  11. hdp

    HiVoltage Testing Station Setup Help

    Check with Hipotronics. They are in upstate New York.
  12. hdp

    SPD in MCC

    Pardon my spell check for incorrectly providing "contractor" for contactor!
  13. hdp

    SPD in MCC

    I have been involved in a couple of situations where a single-phasing event during a storm was interpreted as a "surge" issue. In both cases, the contractor control power was derived inside the customer facility from a 480V-208Y120V transformer. The damage was caused by the reduced voltage on...
  14. hdp

    Hazardous Locations -- Vehicle Maintenance Facility

    You might look at Article 511. It is generally applicable to this type of facility.