  1. HawkBrazil

    2 UPS with one STS

    Dear JBartos, Tks once more about your atention, If I eliminate the CC busbar and maintain only the AC busbar, the SPF only changes your position. Recently I was read one very interesting article at MIL, where they shows the impossibility of elimination of SPF's at all. The only good notice is...
  2. HawkBrazil

    2 UPS with one STS

    Scotty, Yeah, this a old installation where I have a mission of improve the security of the loads at one CPD. Some complementar data: - We have one UPS - 30 kVA - without a by-pass feature.1 ond half Y.O. - We have another UPS - 15 kVA - with a by-pass feature - 6 months old - The...
  3. HawkBrazil

    2 UPS with one STS

    Dear friends, I woulkd like to thanks a lot about that attention. I had one idea, and I like to ask if somebody have tried this before, and if this have success, or not. If I put two rectifiers with regulated output, one for each output of thas ups's that i have mentioned before, then I make...
  4. HawkBrazil

    2 UPS with one STS

    Dear Scotty, Tks about you attention !!!! In this case, I don't need to use a STS. Perfect. The only problem, that I don't have mentioned before is the Upstream UPS don't have a static by-pass ( !!!! ), but the configuration that you have mentioned is possible, due to a downstream UPS have...
  5. HawkBrazil

    2 UPS with one STS

    Dear Friends I have a problem today in Brazil, related with a 2 UPS's and we need to make a transfer of load between that equipments in case of fail of one. In a first moment most of us don't can see any problem, but when you discover of that 2 UPS's are double conversion - not true on line -...
  6. HawkBrazil

    CAN I OVERRUN THE MOTOR TO HIGHER FREQUNCIES?

    Dears, I saw only two problems: 1) What can be the bahavior of the fan, in case of a overspeed operation ? Furthermore, what's the type of fan used - Scirocco ? Limit Load ? 2)All rotating machines, electrical or not, have in a project a parameter called "CRITICAL SPEED". This speed...
  7. HawkBrazil

    Voltage loss control to coil of motor contactor

    Hello Friend, We have a different ways to fix this problem but I recomend, by a better way, one associate between one "time relay with a delay in a de-energization. This equipment, very cheap, can be sold in a different scales of times and may provide other regulations if a half second...
  8. HawkBrazil

    Voltage loss control to coil of motor contactor

    Hello Friend, We have a different ways to fix this problem but I recomend, by a better way, one associate between one "time relay with a delay in a de-energization. This equipment, very cheap, can be sold in a different scales of times and may provide other regulations if a half second...