    Load Dump on Diesel Generators

    Thank you both for your response. We have been load shedding in two stages non-essential and then semi-essential at 2750KW for each. The problem occured when the 3100KW load was seen by the one generator it was not able to recover (actually leveled off at 2620kW) to that load shed mark. It's...
  2. HarlanLSU1

    Load Dump on Diesel Generators

    I have two 2500KW generators online in parallel. If I trip the generator breaker on one thus forcing the other generator to take on greater than 100% rated load what type (KW,KVAr) of load, or combination of, would be best to put on the generator. I believe a power factor less than .8 would be...