When choosing a type of advanced meter to install, would you recommend socket mount meters either directly on or near the transformer feeding a building or would you go for installing a panel mount meter in the existing main distribution panel?
I am wondering about the pro/cons of each setup.
How does one determine the instantaneous trip setting of an MCCB? A software I am using wants me to input the instantaneous trip setting of an MCCB. There is no manual setting that I see though. Isn't this a factory determined level that should already be in the software?
I guess my real question is if the turns ratio can be measured and corrected, and the phase angle error can be measured and compensated for, why are CT's still given 1% accuracy? Where does the remaining error originate?
What I don't understand about the 2 second rule is aren't these questions all about arc flash? Arc flash occurs in an almost instantaneous manner does it not? How then does the 2 second rule apply to anything more than the arc itself?
Looking at a list of fault currents provided to me by the utility, a large hangar with a 500 kva 12.47kv/480v transformer has a fault current of 11kA.
The small building next door with a 150kva transformer 12.47kv/208v has a fault current of 33kA.
These are fed from the same substation. Why is...
I'm running an arc flash analysis and the system has a 60 kVA UPS attached. Upstream of this UPS I am getting numbers of 0.5 cal/cm^2, but I look on the side that the UPS would be powering and it jumps to 136 cal/cm^2.
Is this a common effect of a UPS in arc flash analysis?
I find it...
If I am given a maximum fault current at a transformers secondary from the utility and the transformers impedance, how do I get the fault current that is seen at the primary side of the transformer (in order to get clearing times with the transformers protective device).
Xmfr: 3 phase, 150Kva...
Yeah, I thought I might have to do that. One other quick question. Should the bolted fault current be based on an infinite bus calculation, or the actual fault current?
Hello,
I am performing and arc flash analysis and have run into a problem figuring out what clearing time to use. I am given the bolted fault current at the transformer secondary and the transformer specifications. The 150Kva transformer has secondary of 208V and a fault current of 32000 A. I...