  1. ForeverStudent

    Drainage piping in food service areas

    Thanks a lot, I appreciate all valuable responses.
  2. ForeverStudent

    Drainage piping in food service areas

    Many plumbing codes prohibit exposed drainage piping above food service areas. Is the piping considered exposed if there is a drop ceiling below? If so, would drywall ceiling help? Thank you.
  3. ForeverStudent

    PRV Directly After Booster Pump..why?

    JJPellin, Thank you for the clarification, I thought that riser to upper floors was upstream of PRV. This is let's say ... unusual setup. Pressure reducing valves (PRVs) should be on each floor. Pump needs to be changed in my opinion.
  4. ForeverStudent

    PRV Directly After Booster Pump..why?

    Two questions. 1. How do you know that the PRV (I assume pressure-reducing valve) lowers the pressure back to 200 psi, if you do not have pressure gauge 2. Why do you need 200 psi on the first floor residential? Looks as way too high. 60 psi downstream of the valve seems to be more than adequate
  5. ForeverStudent

    sprinkler booster pump for a part of the system?

    Stookeyfpe, you sited correct section. However I have 4,300 SF on greatest floor, residential floors only 2,600 SF each. I believe that the standpipe is not required in this case. Am I missing something?
  6. ForeverStudent

    sprinkler booster pump for a part of the system?

    Thank you for the valuable comments. Skdesigner, excellent catch. Stookeyfpe, I am in New York City, surprisingly standpipe is not required here if you are below 75' and do not have occupancy more than 30 people above 55' (subject to area limitations though). Could you please mention potential...
  7. ForeverStudent

    sprinkler booster pump for a part of the system?

    Hi stookeyfpe, thank you for the response. I do not have a standpipe, just sprinklers. For cellar I do not need the pump, only for upper floors because of the elevation the pressure of city main is too low.
  8. ForeverStudent

    sprinkler booster pump for a part of the system?

    I have a project for 7 story building with cellar (parking garage in the cellar, two stories medical offices and others are residential). My understanding - for parking garage I have ordinary hazard 1, in other places it is light hazard. My hydraulic calculations show that there is enough...
  9. ForeverStudent

    Sprinkler booster pump rating

    Need to specify sprinkler booster pump for one project. Hydraulic calculations show that 75gpm@50PSI will do the job. But in NFPA20 (Centrifugal pump capacities section) there are 50gpm and next capacity is 100gpm. Do I have to comply with this or for booster pump I can choose 75gpm...
  10. ForeverStudent

    Fire (booster) pump for standpipe

    Hi cdafd, You are correct, normally such a building (residential 6 stories) does not require standpipe, but mine is special case, because of location (narrow street) New York City BSA mandated to install the standpipe.
  11. ForeverStudent

    Fire (booster) pump for standpipe

    Thank you everybody for the valuable input. By the way, as Jomdoeiowa described, what about acceptance test? Does it mean that in this situation it is necessary to physically bring fire truck to conduct the test (with corresponding charges to the client)?
  12. ForeverStudent

    Fire (booster) pump for standpipe

    Travis, as usual you give concise answers, thanks a lot! So as far as I understand in case of wet manual standpipe I do not care about pressure, is this correct? (logically should analyze available water flow though).
  13. ForeverStudent

    Fire (booster) pump for standpipe

    Hi Travis, thank you very much for the response. I thought that in most cases automatic standpipe is required and other types installed only in special situations. Am I wrong?
  14. ForeverStudent

    Saftey Margin

    Recently I was asked by code official for 30% safety margin. By the way, when we talk about percentage, what is the proper way to calculate: delta P divided by available pressure or system demand pressure?
  15. ForeverStudent

    Fire (booster) pump for standpipe

    Hi Everybody, I am in New York, and the code requires for standpipes to provide 70 psi at the most remote connection. The pressure at street level is 55 psi. I did hydraulic calculation and it is adequate for sprinkler demand, it is going to be combined system. Does it mean, that in any case...