I would likely be connecting with a closed delta primary and using 2 transformers. I am trying to arrive the the correct calculations here. Technically, amps are amps, so I would think if the transformer will handle 62A of single phase, that would be 62A using 2 of them on 3P?
Now, I don't...
The books seem to indicate full ampacity vs highest voltage for the kva calculation so 15kva for the values above? unless I missed step.
200V is a standard Japanese voltage. trying to run a Japanese machine in the states. I believe 208V will be just fine and the electronics have another...
I have a situation where I need to buck voltage of 240-245V down to as close to 200V as possible. 200V is not a common voltage in the US so 208V may have to do. I have a couple single phase dry transformers and was considering configuring in a 3P bucking arrangement. I had to look at the...
LOL, we might get to the point of using a genny if we piss off the power company too bad!
On an interesting note, I have a 3 phase, 10HP motor that I tested for fun. Ran it across the line to see inrush, then disconnected it for about 2sec, then reconnected while still very close to sync...
OK, I did some single phase testing at home because I have several phase converters around and already know what they pull and they are easy to test with.
Inrush is all on the single phase side here. All 240V
The inrush seen directly on the dedicated service wire to a 10HP converter = 155A...
I will try to explain more. We have enough 'amps' in the electric service, BUT this is a rural area and the PC has demanded that we not have anything more than 10HP motors on the line. I find it ridiculous, but I will act like I will comply. The way I see it, as long as we are not hitting the...
Waross, it was my understanding that you cannot sidestep the inrush of an induction motor by spinning it to full speed because the coils are not yet energized and still present a low impedance condition when connected? This makes me want to test it though just out of curiosity!
Smoked, I had the very idea about the variac for soft starts but thought I might try to do something more automated. What would you think about some wye/delta switching along with a series choke that would be switched out once up to speed? I cannot remember the calculation of how much current...
Have a few odd question and figured I would roll them all into one.
1. I believe a running but unloaded 3P motor on a electric service has the effect of damping inrush seen by the power company when another motor starts up? IE, the already running motor helps start the next motor. Is...
In tugboats defense, I think he simply means that you cannot simply connect a motor to a load and spin the shaft and make power. You have to excite the coils, but I understand that.
My fault for any confusion. I am asking about specific design differences between an induction motor and an induction generator. I realize an induction motor will in fact generate power, but if one was put to work specifically to generate, how would the design change.
I did look up the...
I am sure there might be some basic adjustments to optimize one or the other like bearings and such, but I was sort of lead to believe there are quite a few differences here? It was my understanding that these are effectively the same thing, just depending on which side of synchronous rotation...
Look at page 24, you will notice two IGBT sets.
Also, look on page 34. There are alarms for the inverter and converter sections.
It is interesting.
Yes, I figure the options would be to slow down decel, or find another way to sync power! I have heard if you have other 3P motors on...
I cannot seem to remember what values we had when we tested the AC line during braking.
I have attached a manual of a drive that we also need to run on the line, but appears it may have line regen? I don't have the general manual, but on page 24 you can clearly see there are inverter and...
Yes, this is a line regen system. Take a look at Okuma drives. Built specific for their own machine tools but do have line regen.
We have the decel rate pulled back but I think we need to look at other ideas.