Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by etchyHA

  1. etchyHA

    weather hourly record data

    hi all is any one knows a site to get hourly record weather data i mean DB, WB , RH temp. i really need it
  2. etchyHA

    cooling water flow rate control

    hi every one well i have a project contains 3- water cooled chiller and 3-cooling towers at and i ve been asked to make a schematic dwg for these equipments ,to control the cooling water flow rate i will use three way valve my question is where is the best location to put is it before the...
  3. etchyHA

    The cooling water thermodynamic analysis ??

    gpm for the condenser u means evaporation load x 1.17 = condenser load say cooling load =600 TR then the condenser load = 702 TR then the cooling tower flow rate = 2106 gpm right? but if i had a chiller the water temprature difference = 16F then the how much the condenser cooling water...
  4. etchyHA

    The cooling water thermodynamic analysis ??

    the cooling water thermodynamic analysis used for cooling water chillers is 1TR=3.5KW= m CPw (twi-two) m= 3.5 /(4.18 x (32-37)) = 0.167 kg/s volume flow rate = 2.65 gpm is that right? cause i know that as a rule of thumb that 1 TR needs 3 gpm cooling water
  5. etchyHA

    PUMP HEAD UNIT mAq??

    THANKS ALOT ZESTI :)
  6. etchyHA

    PUMP HEAD UNIT mAq??

    dear all in an industrial project the chilled water pump is described as 15mAq as head by the designer i cannt figure out what is that unit mAq .i need help
  7. etchyHA

    HAP- EXPERTS I NEED AN INQUIRY

    HI i am using a 100% FA A.H.U. with a cap. of 2000 L/S with heat recovery this AHU IS DX PACKAGE UNIT HAP output data was that the total coil load = the sensible load and it cannot be right ! there is for sure a latent load cause when i changed the type of the AHU to tempering it calculates...
  8. etchyHA

    daikin vrv design soft ware

    why is the outdoor cooling only type is limited capacity comparing to heat pump? the project is at tropical climate i dont need heating applications
  9. etchyHA

    controlling R.H.% by hap-4.3

    dear marcoh R.H. couldnt be controlled at fan coil unit as it doesnt contain demumdifier or reheater so i ve reached that any place needs a certain R.H. i must use a n A.H.U. even if the capacity is small because i ve tried to increase the by pass factor to manipulate r.h i even tried to...
  10. etchyHA

    daikin vrv design soft ware

    hi,, i am using daikin vrv software to design a redential system but i cannt determine what is the difference between cooling only system and heat pum??
  11. etchyHA

    controlling R.H.% by hap-4.3

    yes about carrier software hap-4.3
  12. etchyHA

    controlling R.H.% by hap-4.3

    the hospital areas needs to be served by define air circumistances (r.h.%, temp.,ach...etc) how can i make control R.H. value or make it as an input data at hourly analysis prgramme?
  13. etchyHA

    controlling R.H.% by hap-4.3

    HOURLY ANALYSIS PROGRAMME HAP
  14. etchyHA

    controlling R.H.% by hap-4.3

    hi guys,, the designing of specified areas at hospitals needs a define value of R.H. like 70% the hap define the resultant r.h. on waht bases and if i want to change the relative hunmidity what shall i do? thanks in advance
  15. etchyHA

    steam flow rate and pressure

    thanks HevïGuy but it doesnt include the valuse of steam flow rate for the equipments iam trying to find refrence for steam applications at laundaries hospitals ect... any help?