Chapter 3 article 310.4 states "the paralled conductors in each phase ... shall: a)be the same length b)have the same condcutor material c)be the same size d) have the same insul type e) be terminated in the same manner"
Which one is correct for the following:
- Phase A =OK to have two...
Hi,
What will happen if 4/O and 240mm2 underground medium voltage 33kV cable is paralled? it's used as a part of overhead line 33kV at the beginning of the circuit.
Regards,
Eskim
Hi All,
Our existing generators are 11,000 V +/-5% output voltage. We set AVR 3% above nominal volt (11,350). Gens are running with voltage control set.
What do you think If a new gen 10,500 V +/-5% will be synchronized with existing system. It should run 8% over its nom volt.
Regards,
Sumadi
Dear All,
I have very basic question, but make me inconfidence regard to speeding up induction motor. The existing nameplate is 600kW, 3.3kV and 2965rpm. We have to upgrade the feed pump system by installing VSD to control this motor up to max 3400 rpm. (operating will be 3100rpm)
The question...
Dear All,
Please confirm me for this small confussion. Can I use non-insulated 600V terminal lug to be used for 11kV arrester circuit ? In my opinion Yes, since voltage will effect to insulation material only so for non-insulated doesn't matter.
Thank you all.
Sorry, I am not an active member of this forum I just open this if i have problems.
My calculation showed (-) sign since the angle of current are not in correct direction I think.
I have to correct CT connection for this relay, and will come up eith the result next time ?
Hi,
I am calculating 3-phase power with these datas, all value line-to-line:
Ia= 782.831 @184.8 deg
Ib= 792.247 @306.9 deg
Ic= 763.033 @66.4 deg
Va= 10.973 kV @0
Vb= 11.005 kV @119.9
Vc= 10.990 kV @240.1
3-phase Real Power = ???
Anybody can help me ? Thanks all.
What does NPS (voltage/current) mean?
"BTW, we had thread on the topic."
What is the topic subject title..?
Can I use 59G relay with input comes from broken delta PT tapped from 400V line directly?
Eskim
Dear All,
Sorry if this question has been posted before, I have found 2 thread about E/F protection on D-Y transformer, but not cover my question below.
1. We have experience Hi-Z fault on LV(400V) O/H line which is supplied by 11/0.4kV Delta-Star with solid grounded pole XFMR around 50kVA. At...
The exciter is staked from PMG/pilot exciter --> AVR --> exciter stator --> exciter rotor --> finally to main field winding. The broken diode and thyristor is at the exciter rotor put in generator shaft, unfortunately I can't attach the drawing.
In the normal running with 27MW (our Turb Gen is...
Dear All,
I've problem above for the last two days. The six-pole, full wave rectifier have one diode and thyristor broken at the same time. We have over current and over voltage relay picked up at excitation control (V~4000V and I~40A).
My question:
1. Why the current and voltage at excitation...
Guys,
I am looking for transformer oil purifier equipment will be used to purify 19000 ltrs of oil contains.
Anyone could recommend Manufacturer of oil purifier, please forward ro me.
Thank you all.
Rgds,
Eskim
Dear All,
What is the based difference between AC and DC HiPot tester. When I test HV equipment e.g. Surge arrester, cable, generator winding, etc. What is the best method using ac or dc tester ?
Some one told me that mA is the "most important" to select DC or AC ? I didn't understand what...
Dear All,
I am not experience in T&D. But our transformer using Lightning Arrester on HV connected to transmission line. How to get proper spec of arrester for this transformer (theory, calculation, standars, etc).
Also the LA is connected with discharge counter(?) what is the function of...