    YD interposing CTs for Trafo Plain Balance (Differential) protection

    slavag, I used to work in IEEE world earlier and this concept is also new to me but as I mentioned earlier, I am now in UK and this is a backup protection. There is a already a combined diff biased and HV/LV REF protection (Duobias Relay) as main protection. Plain balance is a standard back up...
  2. EPEngineer

    Buried cable calculations.

    breaker 12 If you are in IEC world the applicable code would be IEC-287. Sometimes the clients are happy with cable sizing calculations based on current capacity for specific laying conditions and applying different de-rating factors which are clearly mentoined and explained in cable...
  3. EPEngineer

    YD interposing CTs for Trafo Plain Balance (Differential) protection

    jghirst / slavag, Many thanks for your responses. I must confess the scheme is not correct, excuse my drafting techniques. I have uploaded another one. The relay used is P122 Micom series relay. 5:1 interposing CTs shall be used to balance 2000/1 to 2000/5 LV sides as one is existing. The only...
  4. EPEngineer

    YD interposing CTs for Trafo Plain Balance (Differential) protection

    Hi, I am involved in protection scheme design for substation in UK. We have a plain balance scheme similar to a high impedance differential scheme for trafo protection but as a back up so thats why 5P20 CTs and interposing CTs are used. 3 Wdg trafo vector group is Yyn0yn0. It is a common O/C...
  5. EPEngineer

    Mesh Corner Arrangement & Protection for EHV

    Could anyone please educate me (or refer to a book / link) about EHV Mesh Corner arrangement and protection principles? Regards
  6. EPEngineer

    Shielding / Grounding of OH Oil & Gas Pipe Lines

    Hi, Is there any international (European, American or British)standard which describe the method of providing lightning protection for overhead oil and gas pipe lines? I have come across 800 meter long pipelines laid on 17meter height overhead pipe racks (reinforced concrete structure) carrying...
  7. EPEngineer

    Grounding grid current flow back to source

    Thanks jghrist, I am using CEDEGS software by SESTECH. There are several modules with different capabilities. In a nutshell, it is not possible to model the two grids with return path in that software as there are lot of coated conductors as well. SES helpline told me that I could ignore the...
  8. EPEngineer

    Grounding grid current flow back to source

    Sorry David, ECC stands for earth continuity conductor. I should also mention that I am in UK.
  9. EPEngineer

    Grounding grid current flow back to source

    Hello everyone, I have a situation here regarding grounding. There is a new 2x132/11/11kV substation fed by 2x132kV cable circuits. Cable sheaths (95mm2 each) are connected at both ends, length is only 4200m. We also have 2x150mm2 ECCs connected at both ends. Cable sheaths and ECCs are within...
  10. EPEngineer

    CT sizing for transformer overcurrent application

    Does this surprise only me? I would be more surprised if in IEC world someone would ask you to do so ....
  11. EPEngineer

    British Standards Graphic Symbols

    giuseppe I am not sure but I think IEC 60617(1-13) 1996, is the current British graphic symbol standard. At least the copy I am having says so.
  12. EPEngineer

    CT sizing for transformer overcurrent application

    Are you sure you are going to install CTs for O/C protection on a 200kVA transformer on 11kV side? Genarally transformers of this capacity are protected by H.V (or M.V) Fuses. However in IEC world IEC-185 and IEC-44-6 are the standards for CTs. Regards
  13. EPEngineer

    Difference between Class PX and Class X CTs

    Could anyone please educate me with the difference(s) between class PX and class X CTs? What are the related standards, if different? Regards
  14. EPEngineer

    Additional Check CTs for double bus bar proection