waross,
This was what we were doing. Full load at secondary 2.25 MVA (half of primary winding) and use as base 2.25 MVA at primary. We was in doubt in what MVA base to use (2.25 or 4.5 MVA), but considering what 7anoter4 said, now, I really think that I should use 2.25 MVA in all three...
waross,
This was another pointing of discussion here, during de transformer testing.
I'm not sure what base use in primary winding, 4,5MVA or 2,25MVA. Until the moment no one coul answer this for me.
First I was thinking that correct is use 4,5MVA, but another guy here said do use 2,25MVA as...
Thanks a lot, pwrtran.
13.89 kV was a typing error. The correct is 13.8 kV.
We was calculating Zps and Zpt like in your first answer, founding 9.05% and 9.04% respectively, assuming that power base por HV winding was 2.25 MVA (half total), for a full load in secondary OR tertiary winding.
My...
Hi, all.
We are testing a new three winding transformer (4,5 MVA 13.8 kV Delta / 2,25 MVA 0,48 kV Wye / 2,25 MVA 0,48 kV Wye) to obtain the percentual impedance of windings. We obtained the following results:
-Voltage applied in 13.89 kV winding with secondary short-circuited and tertiary...
Hello everybody.
I was looking for AVR models to install in a 25MW 13.8 kV generator, for an industrial usage.
We are substituting the old AVR's units by new ones. What are good manufacturers for this products?
Best Regards!
Hello.
Can anyone know where I find the demo version of Siemens DIGSI 4.0? I was trying to install 4.83 demo version, but it was required de old version first. Thanks.
Thanks waross.
Reactive power demand at induction motor starting is about 15 MVar (0.2 PF estimated at starting). I'm not sure if SM can generate 15MVar. PF protection is set with 0.7 inductive with 0.2 seconds. It was adjusted in compliance with IEEE C37.96-2000 - IEEE Guide for AC Motor...
Thanks, dpc.
Actually, we have tried to change SM to a overexcited mode, but it didn't work. I think that SC limiter impedance is high, and so IM drains from a lower impedance source, in this case, the synchronous motor. In this way, i'm not sure if operation with generators A and B will solve...
Hello.
In our industrial plant, we have some problems during an induction motor starting. I'd like to talk about ideas to solve this problem. The electrical diagram is attached.
Describing the problem:
Two generators (A and B) connected in two load bars (A and B) that connect to a...
Thanks a lot for the ansers. Now I am uploading graphical oscilography of phase currents, differential currents ans restriction currents.
Only by information, relay is a SIEMENS 7UM62.http://files.engineering.com/getfile.aspx?folder=38aaa3f7-c4e0-495d-85d8-4c1c4f982cdc&file=iA,_iB,_iC_currents.JPG