Recent content by elmatador

  1. elmatador

    Diesel Genset Transformer Inrush

    Thank you kindly for your feeback. This particular setup is for a 600V system. The main generator breaker and ATS breakers are 600V 1200A 100% And come with electronic trip units with adjustable long time, short time, and instantaneous settings. The dry type transformers have thermal magnetic...
  2. elmatador

    Diesel Genset Transformer Inrush

    We are currently inplementing a design with a backup diesel generator which is used to backup critical loads in a facility. The generator is a CAT C32 PMG 1MW Standby, 1.25MVA. The generator is coupled to a traditional ATS with open transition transfer. When utility power is lost, the ATS will...
  3. elmatador

    Arc Flash Mitigation

    wbd, thank you kindly for your insight on this subject. I managed to find the equivalent verbiage to NFPA 70E-2015, Table 130.7 (C)(15)(A)(a) in the Canadian CSA Z462 which is derived from NFPA 70E. The CSA document states the two methods, (1) Incident Energy Analysis, (2) Arc Flash PPE Category...
  4. elmatador

    Arc Flash Mitigation

    The end user has the perception that the main breaker on the MCC can be set to maintenance mode when the downstream feeder breakers on the MCC is being operated. Their take on it is that they should be able to set the main breaker to maintenance mode while energizing feeder breakers on the MCC...
  5. elmatador

    Arc Flash Mitigation

    Wbd, yes an arc flash study has been done and the incident energies have been calculated. There is room to increase the pickup level during maintenance mode and still be within acceptable incident energy values.
  6. elmatador

    Arc Flash Mitigation

    Hello, I had a question with regards to utilizing the arc flash mitigation maintenance mode switch on a low voltage circuit breaker. Should the maintenance mode setting take into consideration the energization of a large load downstream? For example, the MCC main breaker has the maintenance...
  7. elmatador

    Motor Diff. CT Wiring: 4-wire Vs 6-wire

    Thank you David for your comments on this subject. I see your point. We will be running a 6 conductor cable for this. We will end up having to add additional terminals on the MCC end as the vendor has configured the field connection as a 4-wire.
  8. elmatador

    Medium Voltage Motor Conductor Temperature rating

    Hi there We have several 4000v 3000HP motors which are fed from a Siemens MCC FVNR cells. My understanding is that medium voltage equipment is suitable for 90degC terminations where the ampacity of the conductor can be based on 90deg ampacities. How about the motor end? These are API 541 motors...
  9. elmatador

    Motor Diff. CT Wiring: 4-wire Vs 6-wire

    Thanks for your post David. Is this mainly because this is a differential application where you wouldn't necessarily see a balanced output if there was an internal fault on the motor? Why is it in Switchgear's that the neutral on the phase ct's are commoned up together and grounded? Wouldn't...
  10. elmatador

    Motor Diff. CT Wiring: 4-wire Vs 6-wire

    Hello all, We have a few medium voltage motors with a 50:5 core balance current transformer for each phase. Are there any issues with connecting the neutral of each CT together at the motor end so that you only run 4-wires back to the relay, where the fourth wire is the common neutral wire? Are...
  11. elmatador

    Motor Start HPS lighting dip

    Thank you kindly for your response. I managed to get the crouse hinds ballast data and their dropout voltage is 80%. So should be safe.
  12. elmatador

    Motor Start HPS lighting dip

    Hi Folks, I am carrying out a motor starting study. I have a 3100HP 4000V motor being started across the line at a system voltage of 4160V. Motornis a centrifugal with closed valve start. The main transformer is a 12MVA transformer. The voltage dip is 13% for 1.5s. This dip is also seen on the...
  13. elmatador

    Motor Protection Self Balancing Differential Current Transformer

    Thank you kindly for your response! Much appreciated!
  14. elmatador

    Motor Protection Self Balancing Differential Current Transformer

    Hello All, We have a several 4kV motors, horsepower range is anywhere from 2000HP to 3500HP. These motors come with 50:5 self balancing differential CT. The accuracy class of these CT's is C10. The worst case distance of the motor from the Multilin 469 Motor Protection Relay is 180 meters. I am...