  1. elham02

    ASME U Stamp for Vacuum operated Steam Surface Condensers

    Dear Mike, Thank you so much for the support. Regards
  2. elham02

    ASME U Stamp for Vacuum operated Steam Surface Condensers

    thread404-306554 OK, SnTMan stated that the tube side can be exempted under U-1(f). U-1(f) addresses the pressure relief devices. Can anyone help where it can be found in the code (July 2013 revision) ? Thanks
  3. elham02

    Generator Stator Damage incident

    Thanks mr.Waross for your contribution, what I was trying to point out is as follows: There are two situation of out of phase synchronization; the generator ether leads or lags the grid. The synchronizing circuits differ, some circuits if you reverse two wires you will end up with an error of...
  4. elham02

    Generator Stator Damage incident

    Hi all, Sorry for the delay, I could not access any of the data, the case is under investigation by the OEM. Mr.Pikoplatt The IR values are in order before and after. You mean by stator cables the termination? No it was not removed. Generator Breaker: what do you mean by removing the...
  5. elham02

    Generator Stator Damage incident

    Thanks for your thoughts Out of phase closing, I have thought about this, will the out of phase closing cause a circulating current in the double winding of each phase? Regarding GE, I would prefer to stay neutral in my opinion about all manufacturers... And for the synchronizing scheme...
  6. elham02

    Generator Stator Damage incident

    Dear David This is not the first unit. 10 units are in-service without any problem. And if it was setting problem how do you explain the Buchholze relay operation? Posting the events… sure…but I think the osc.is better since it will show the currents and voltages waveforms. There was a severe...
  7. elham02

    Generator Stator Damage incident

    Hello, Background: During a scheduled unit SD, the generator rotor was taken out and the stator goes under rewedging and retaining rings replacement process. In the mean while the old protection panel was replaced with a new numerical one. Incident: When we synchronized a 153MVA generator...