Recent content by ELEP

  1. ELEP

    Zero reactive power function

    Thank you so much 'esee135' for posting detail explaination. Now my doubt is clear, with present 776MVA generator we have this function, I have investigated few older generator where this function is not there, as you suggested we can retrofit old AVR with new one.
  2. ELEP

    Zero reactive power function

    thanks ! esee135 What I understand is that before isolating generator from system during fault or shutdown condidions Zero reactive power function will be activated so that only active power current will be interupted by circuitbreaker, Which can save wear on breaker. One more question, is...
  3. ELEP

    Zero reactive power function

    j3n5, you are right! the manual says that, 'An unloading facility is available which, when activated, will reduce the generator reactive power to zero or the power factor to 1,0.' perhaps it may be generator open condition. thank you so much!
  4. ELEP

    Zero reactive power function

    Thanks! tlrols, there is separate power factor control function in addition to Zero reactive power command in AVR. I have encountered this(Zero pf) command in 270MVA as well as 776MVA Generator. I am doubtfull if they are usually using this function.
  5. ELEP

    Zero reactive power function

    Hello Eevryone! I have come across one of a 'Zero reactive power function' while reviewing AVR document for 776MVA Generator. In AVR manual this functions is not described in detail. After googling few websites I found this function is incorporated in Power controller(VAR controller for...
  6. ELEP

    Generator Capaility within voltage limits

    Yes, 11.5kV tap can be considered as nominal tap for transformer. Many Power plats have ratings like this, Generator nominal voltage rating 11kV & Genr. Tfr. nominal voltage rating 132/11.55kV(5%more). It is General practice to keep nominal rating of Gen. Tfr. 5% more to compensate full load...
  7. ELEP

    Fast Bus transfer in the power plants

    ScottyUK; Simultaneous, closing command for bus-tie and the opening command for incomer under detection of loss of voltage, under fault condition need to confirm CB open. There is facility in HSTS, we can programme logic upon loss of voltage & under fault condition. Under fault condition...
  8. ELEP

    Fast Bus transfer in the power plants

    ofcourse there are many conditions to be verified to close tie-CB; loss of incomer voltage, incomer current, incomer CB aux. contacts etc.., even protective relays which blocks HSTS operation.
  9. ELEP

    Fast Bus transfer in the power plants

    We provided ABB's HSTS(High speed transfer system)'SUE 3000' system which makes it possible to obtain transfer times equal to 100 ms with the use of all conventional circuit-breakers. With HSTS system for three circuitbreakers(Unit, Station & Bus-tie): when the loss of voltage in one of the two...
  10. ELEP

    Soil model with out intended resistivity values

    As soil is excavated and the same soil will be backfilled then there is no question of change in soil resistivity. But, possiblity can't be denied that backfilled soil may have higher resistivity initially, the reason is backfilled soil is not compacted so it forms cavities which may contain...
  11. ELEP

    Power plant earthing design

    jghrist: Breaking ground grid area is not going to reduce sufficient overall grounding resistance. But to take care of step, touch potential in areas where personnel are expected to be working. I want reduce spacing, use more ground rods, use some backfilling material etc.
  12. ELEP

    Power plant earthing design

    rcwilson: Thanks for detail reply. I am going to consider all your mentioned points while construction. But my client wants precalculation of 5ohm. To satisfy clients requirement, I am planning to break up ground grid area in to no. of parts such as Transformer area, Water treatment area...
  13. ELEP

    Unit main transformer sizing?

    thanks:bacon4life Transformer loading is nicely explained in IEEE C57-91, I think it can be easily applicable for distribution transformers. Grid connected and generating transformers are always running on full load I believe, and they are desigend like that I think.
  14. ELEP

    Power plant earthing design

    Hi everyone, I am designing an earthing system for 240MW power plant, the area is 230x720m, average soil resistivity 14,000ohm-m(Sedimentary rock), fault current 20kA. I used 120sqmm cooper condr with 15x15m spacing, 0.5m depth. With this data I am getting ground grid resistance 9 ohm, GPR more...
  15. ELEP

    Unit main transformer sizing?

    thanks! :KH2 yes! IEEE C57.116-1989 is very helpfull.