Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by eleecsunil1965

  1. eleecsunil1965

    Manholes for electrical cables enetring building?!

    Is there any standard which specifies the requirement of manhole before the underground power cables enters building Main switch board room?Is this is standard industrial practice?In one of the Industrial control room building project i am doing in middle-east, designer/consultant has proposed...
  2. eleecsunil1965

    Current transformer size

    AS i told before only concern is protection requirements.Thanks stevenal.
  3. eleecsunil1965

    Current transformer size

    Connected load will be around 300KW on 480 volts bus(lighting, small power and HVAC units( maximimum motor size 20KW only. Fault rating on 13.8KV side bus is 500MVA.I am concerned about only protection relaying purpose. Metering is just for indication purpose only.
  4. eleecsunil1965

    Current transformer size

    We are trying to use one spare feeder for energising one new Transformer(750KVA,13.8kV/480Volts,60Hz.6%(Z), using feeder 1200Amps,breaker(VCB) having 600/5, ANSI C200 class current transfomer(Bus bar mounted) for protection relaying and measuring purpose. Is there any accuracy issue with this CT...
  5. eleecsunil1965

    Hermetically sealed tarnsformers or conservator type transformers?

    Is there any Inernational standaards that specifies requirements of conservator type or hermetically sealed transformer to be manufcatured or used?I mean for oil cooled(ONAN) transformers any specific requirements which type to be used?Or is it user specified requirements?What is stanadard...