Good morning Support
Any experience with STAHL HMI model :EXICOM ET-416-FX.
After re-initiating power to the control panel HMI didn’t boot up. When powering up , the HMI emits 4 beeps and LCD doesn’t power up. Failed HMI was removed from the panel and bench tested in workshop with identical...
Thanks Danw2 for taking time on this.
In the meantime we have also received a confirmation from our vendor saying this isolator/splitter is not correct type for our application i.e wrong parts were installed inside control cabinet.
Hello Support,
I'm on site trying to commission application with several Allan Bradley isolators model 931-TD002. This is a new system not being tested before.
Isolators were installed to isolate/split 4-20mA signal into two outputs.
As per dwg. we are simulating signal directly to isolator...
Its four years old application and just a month ago we started to deal with that problem.Application is still running without any problem but it’s quite annoying to have that alarm popping up all the time at our scada and drive screen.
Grounds and shields are connected as per manuf. drawings. Cables coming into enclosures are not unnecessary coiled. Motors are close to 330ft far away from VFD drives and motor power cables are in separate cable tray.
Encoder cables are in cable tray together with 24V DC solenoid cables...
Hi,
I've got following problem -hope somebody can help- any input would be much appreciated
Machine runs with two motors powered by (ABB ACS800 drives) in master/slave configuration
On master drive we have intermittent encoder error (7301) which is popping up at motors low rpm and sometimes...
Mohsen,
If your sensor is labeled as EEx d [ai] that means you have intrinsic safe associated component inside flameproof box.
You are allowed to install it in all three zones 0,1,and 2.
Certified barrier gland is mandatory on junction box.
Sensor, power supply etc. all must be connected as...
We are dealing with mud tanks as well, and believe that ultrasonic sensors are the best solution.
We use Prosonic M type,it's very reliable and work's perfect.Float devices are not the best solution,neither pressure transducers especially if specific density of the mud is changing
That is a type of protection that limits the energy available in the hazardous area to the level below that which could ignite a flammable atmosphere as itsmoked described.
2 types of barriers used in IS circuits:
Zener barriers and galvanically isolated barriers.
Zener barrier must have earth...
Slavag as per your link from April.2003-March.2004 Dell manufactured motherboards for those computers with "faulty" components. We received our computers in November.2004 !
Any way different type of new computers is already installed.Lets see what will happen.
Also like LionelHutz mentioned my...
Hi Salvag
computers are dell GX 280 Optiplex
ups - Powerware3 105
That is what I was thinking.may be just serial/type problem.
But they have been working ok for almost 3 years and then suddenly they all burned in short period of 5-6 months!
Yes all computers are connected to communication switch.communication switch has its own separate ups.Ground should be on the same potential as grounds for computers power!
Are you trying to say that some voltage spikes can be induced in net (CAT) cable and that can be the reason of burned...
Thanks for quick reply’s
Computers are already connected to ups.Each of them has its own ups.
About DC power,yes it is old 6 pulse.I will have a look in all this