  1. elecquest

    Volt drop from transfo to shed

    thanks everyone for prompt reply and explanation!
  2. elecquest

    Volt drop from transfo to shed

    Another thing .. voltage drop in the neutral conductor stands too? as mentioned by bacon4life .. it would be 4.9*2 = 9.8V?
  3. elecquest

    Volt drop from transfo to shed

    wow, thanks very much .. very informative!
  4. elecquest

    Surge arrester on neutral terminal of transformer

    Never heard of this but would be glad to get some explanation as well ...
  5. elecquest

    Volt drop from transfo to shed

    Oops, Burnt2x .. i mean i have to supply the shed with 1 phase power supply only (230 V : PHASE-NEUTRAL) .. If you have more questions, write it , perhaps i am missing something
  6. elecquest

    Volt drop from transfo to shed

    Ah yes thx :P They are tungsten lights at the far end and the 70 mm2 cable is Aluminium .. Mistake: 415 V instead of 415kV in original post ..ack Phew .. just started working as an engineer :| Takes a lot of focus Thx for the support! cheers
  7. elecquest

    Volt drop from transfo to shed

    Hi Could you please correct me if i am wrong? I have this situation: To supply a shed 1.3 km away from a distribution transformer (22 kV/415V - three phase)on 230V, load = 1kW. 415 kV cable used = 70 mm2 - three phase. V/A/km of 70 mm2 cable = 0.87. Volt drop up to shed = 0.87 x 1.3 km x 4.4 A...
  8. elecquest

    Clearance 66 kV

    Thanks! i'll check it out :)
  9. elecquest

    Clearance 66 kV

    Hi I would like to know the clearance distance (vertical and horizontal) to be kept from 66 kV pylons (metal lattice towers) to buildings please? Thx