Dears,
we have 2X20MVA power transformers 66/33 KV WORKING IN PARALLEL TO FEED AN ELECTRIC ARC FURNACE
(WORKING THROUGH INVERTER )AND ITS AUXILURIES&UTILITIES, THE TOTAL LOAD IS 35MVA, WHAT ARE THE RISKS AND POSSIBLE DANGEROUS
INVOLVED IN CASE OF ONE OF THE TWO TRANSFORMERS FAIL, AND WHAT'S...
THANK YOU SO MUCH SCOTTYUK,
(You might consider supporting local generation by operating in parallel with THE utility)THIS IS WHAT I
PERSONALLY PRACTICED IN A PLANT THAT HAS 20MW STEAM TURBINE FOR LOCAL GENERATION WORKING IN PARALLEL WITH THE GRID, BY ADJUSTING THE LOAD SHARE CONTROL OF THE...
dears,
I found this paper gives good ideas regarding the case we are discussing.https://files.engineering.com/getfile.aspx?folder=a1ab033c-4938-4e4c-9235-3a9537863469&file=2_36.pdf
what I understand from the answers:
1- most of the colleagues are not in favor of an isolated system of diesel generators.
2- am thinking about turbines, I mean isolated combined cycle power plant has 2.5 power capacity
more than the EAF.
3-the turbines will be equipped with a highly responsive...
DEARS,
DUE TO LACK OF ENOUGH WATER, I DECIDED TO GO WITH DRY COOLING INSTEAD OF WET COOLING
FOR OUR COMBINED CYCLE CONDENSING STEAM TURBINE, FOR A SURPRISE I HAVE BEEN TOLD THAT I NEED
TO MODIFY THE ROTOR VANES IN THE REAR SIDE OF THE TURBINE.
IS THIS TRUE? IF YES THEN WHY?
Dears,
we are discussing the case of supplying power from a 230 MW combined cycle power station directly to a 100 MW electric arc furnace, the power station is connected to the utility grid, because utility put on me some restrictions to operate the furnace on the grid, I convinced the power...
why it is more difficult to connect a combined cycle power plant to loads than
connecting it to the utility grid and what is the best way to connect the isolated power plant to
the loads?