  1. eengK

    VFD used as a SS

    davidbeach, That is an excellent point, I would have to say that there would be no way to transition away from the VFD that I could see that would prevent what we are trying to solve in the first place. Essentially they want a VFS (variable frequency starter) but that doesn't really exist...
  2. eengK

    VFD used as a SS

    Hello, Here is the situation, I am having a debate and am trying to determine if it is possible to use a smaller rated VFD then one that would typically be installed for a given load to be used solely as a soft-start for a large compressor. The utility requires a small inrush current that...
  3. eengK

    Distribution voltage drop over distance

    Turns out the line is to be Linnet ACSR, in a typical T pole construction with 88" spacing between the furthest conductor and the middle one in the center @ approx 5" height. After looking up the specs on the conductor here...
  4. eengK

    Distribution voltage drop over distance

    desrod, Thank you very much for that!
  5. eengK

    Distribution voltage drop over distance

    It will be a 3 phase, but no knowledge yet on PF. Thanks for the input dpc. I will give those books a look over. I guess I was looking for a rule of thumb or a basline to use for approximate voltage drop over given lengths. Stictly for observation purposes.
  6. eengK

    Distribution voltage drop over distance

    davidbeach Normally I think you would need to know the code name for the conductor and for a 336 kcmil I beleive there are a couple choices : Merlin Oriole Linnet ... Ok so stay with me here, if we select Merlin, we know R(AC@75C) = 0.0625 ohm/1000ft 519 allowable amps then I would think...
  7. eengK

    Distribution voltage drop over distance

    Hello, I am trying to figure out a rough calculation of the voltage drop of a 25kv, 336 kcmil ACSR conductor over given lengths (40km or more) from 2 8MW feeders. It has been a while since I have touched this stuff and can't remember the equations I should consider for a rough estimate or any...