Recent content by dumor

  1. dumor

    NFPA 14 Class I Manual Combined Standpipe

    FYI...and although not shown on the Flow Diagram, All pipe is 6" and 4". 6" feeding 3 connections, 4" feeding everything else.
  2. dumor

    NFPA 14 Class I Manual Combined Standpipe

    Cdafd, Tried to convince the FD that the 100 psi static city pressure in addition to their 2500GPM booster pump (Hale Qmax)on thier 300Hp Engine should be more then sufficient to meet anything they wanted. Unfortunately and for some unknown reason, the FM is only allowing us 150PSI at the FDC...
  3. dumor

    NFPA 14 Class I Manual Combined Standpipe

    Taken literally, NFPA 14 7.8.1 and 7.8.1.1 clearly states "100psi at most remote or top most outlet." Not all. I understand that in a vertical standpipe due to elevation, 100psi is implied as available at all connections, but at "any and all connections" and at the same time? I just have a...
  4. dumor

    NFPA 14 Class I Manual Combined Standpipe

    It is a Class 1 Combined per NFPA 14 in a County Jail w/ an I-3 occupancy and the local FM's interpretation of 905.3.9 of the (Ca) CFC 2007 for a "Class 1 Standpipe System ...provided in all areas where 50 or more inmates are restrained". Given this, three Separate Detention Pods meet this...
  5. dumor

    NFPA 14 Class I Manual Combined Standpipe

    Here's the current flow diagram. http://files.engineering.com/getfile.aspx?folder=787d59eb-bb5b-4393-a9f0-116083af4bde&file=South_Standpipe_Calc_REV3_RFD_061611_Model_(1).pdf
  6. dumor

    NFPA 14 Class I Manual Combined Standpipe

    The Fire Department is only allowing 150 PSI from their Truck, and the most remote Connection is 1200 ft away. I can Prove that each has valve can deliver 100/250 w/ 250 flowing as allowance at each of the other connections, but not 100/250 at all simultaneously.
  7. dumor

    NFPA 14 Class I Manual Combined Standpipe

    Does it matter where the Hose Connections are in relation to one another? Seperate Fire area, Building Etc?
  8. dumor

    NFPA 14 Class I Manual Combined Standpipe

    Yes...this is where it gets a bit tricky. The Stdp System is a Horz. type and is Combined with 2 Wet Pipe Sprinklers. Of the three Hose Valves, One Connection comes off one of the Wet Sprinkler Sys and Two Connections come off the other. They Share the FDC. All three valves are at the same...
  9. dumor

    NFPA 14 Class I Manual Combined Standpipe

    Sorry...fairly new at this. My Question is, Is it the intent of 7.8.1 to require 100PSI at all outlets simultaneously, or just the one most remote..?
  10. dumor

    NFPA 14 Class I Manual Combined Standpipe

    Per 2010 NFPA 14, 7.10.1.2.2 I'm providing 250 Hose allowance at all three (3) 2-1/2" Hose Connections of a Class 1 Standpipe System. per 7.8.1, I'm providing 100psi at the most hydraulically remote single 2-1/2" connection. The System is Manual and Combined with two separate Wet pipe Sprinkler...
  11. dumor

    Calculation procedures - Light Hazard adjacent to Ordinary Group 1

    Enough said. Albit it's helpfull to know what the design standards are ahead of the question.
  12. dumor

    Calculation procedures - Light Hazard adjacent to Ordinary Group 1

    What was the verdit on the space above? Why the 3000?
  13. dumor

    Calculation procedures - Light Hazard adjacent to Ordinary Group 1

    Why the 3000 sq ft design area? is there a unsprinklereed comb blind space above? If not, and the mechanical rooms doors are self closing and 1 hr rated then the calc area culd be limited to the room size. If you have to calculate 3000 sq. ft because of the un-sprinklered space bove, then the...