All i find on the two is this:
THW (5) 75¡C 167¡F 90¡C 194¡F
DRY & WET LOCATIONS SPECIAL APPL. WITHIN ELECTRIC DISCHARGE LIGHTING EQUIPMENT LIMITED TO 1000 OPEN-CIRCUIT VOLTS OR LESS, (SIZE 14-8 ONLY AS PERMITTED IN SECTION 410-31).
MOISTURE AND HEAT-RESISTANT THERMOPLASTIC
THWN (5) 75¡C...
So, if I am going to install the following:
Three (3) single phase 480 to 240/120 25kVA transformers
One (1) single phase 480 to 240/120 10kVA transformer
One (1) 15 HP 480V 3PH motor
What size "three phase transformer" will I need?
Does this chart i put together look right for what I'm...
Thank you. So to clarify, if there is only 40A of load at 240V will the 480V side of the transformer (fed by phases A and C) see 20A on each phase or will it be split between the two (A = 10A and C = 10A)?