Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by don01

  1. don01

    wire insulation under screw terminal

    ah well er um ..... few words can describe that workmanship (that can be printed in public.) This is why most industrial projects specify crimped terms. If you are OEM then you are just buying warranty claims , If you are client side then YOUR projects are going to be unreliable with...
  2. don01

    Megger testing 600V wire at 500VDC

    JacksonJim split this into 2 issues 1. a cable was tested and there is debate around the voltage used..... more later 2. A cable was tested and passed the test - I am not keen on the voltage the test was done at BUT IT PASSED and was good when the meter was disconnected. -I hear "the you...
  3. don01

    Earth grids and hard drawn copper Vs annealed copper

    Thanks desertfox, jghrist, Kiribanda I really appreciate your responses. It would seem we can give a little push back here and ask to use the available materials (desertfox, these are laid very loosely in the trench and covered with conductive sand & soil mix there should be no creep or forces...
  4. don01

    Earth grids and hard drawn copper Vs annealed copper

    Hi All We are building a 132KV/33KV substation. The designer has specified the conductor for the grid to be 150mm2 uninsulated multistranded HD copper. The inevitable supply issues has drawn out the response " we have lots of annealed available lets use that" we have not done so (we'll wait for...
  5. don01

    Arc Flash disagreement

    hi all I live under a different set of rules awhere limits of approach are set for all access to area. So this conversation is acedemic to that but lets take a step back - You & I have a duty of care to all in our charge & those around us. If we dont have enough ppe for the tourists then they...
  6. don01

    power required to lift a mass

    hi all Pete ,as usual, is on the money again. But here it is straight from my physics text book (which is soooo old it is a national relic) PROBLEM: a plane weighing 5000kg can climb vertically at a rate of 200km/hr. What power is expended. (9.8m/s) SOLUTION: power = work/time = (force x...
  7. don01

    PID output staying High when SP = 0

    hi all at the risk of sounding trite the simple fact is this is a PID controller. It is bad practise to use an auto setting of 0 to force the output to drive closed. You will have an indeterminate position occuring and the controller will ramp (yes reset windup) to some undefined position. AND...
  8. don01

    Very low power miniature motor control

    how about looking at itsmoked & pluckers sensing ideas?. - something like a coil or pick up on the side of the motor. It should be as noisy as hell when moving and quiet when not. Amp or switch the "signal" back to the PIC ? but:- enjoy trying Don
  9. don01

    Instrumentation Problems

    hi all It is implied that you have analog inputs for both flow & pressure . If not get it. From this point the spread of pressure / flow rate is quite calculatable. If you have a pipe rupture the pressure will fall below a deviation alarm and alert your operations. If the pipe is blocked or...
  10. don01

    Power transformer vector designations

    unclebob & cuky2000 Thanks guys - a collective "ahhh yehhh that's right" has eminated out of the office and now there are dull thud sounds as reference books hit the desks. your replies really appreciated and have stimulated a lot thinking here Don
  11. don01

    Power transformer vector designations

    We have a list of suitable transformers for our job but the vector designation has us scratching our heads. What does "Dyn11" mean. we assume "D" = delta primary "y" = star secondary with nuetral but what the is "1" or "11"? knowing we make look a little sheepish but thanks in advance
  12. don01

    raser

    oh yee of little faith!!! now my grandad dint think that new fangled eltrizinty stuff could amount to much. you know pushing smoke thru wires how's that gonna cure any ills. but then again I dont think I'll buy shares either (ps it's obviously smoke cause every time you break the wire theres a...
  13. don01

    squirrel cage motor power factor

    thanks all True to form this gruop of dynamos has the answers. (that is a really bad pun, hey?) Marke,that is probably the bit our debate was missing again, thanks
  14. don01

    squirrel cage motor power factor

    We have been having a discussion on the relationship of load and power factor in squirrel cage motors. Generally it is agreed that pf. improves as the load approaches 100% BUT nobody can find a graph or curve on paper. Does anyone know of a site or link with this available. We have done a bit...
  15. don01

    Eight Digit Totalizer

    oldpfart seems to be the closest to my guess. The modicon could well be one of those PLCs that only support integers. You are incrementing a data register for each unit passed. If you check the manual you may well find that the maximum value for an integer is 65535If this is the case look to...