Well in bridge engineering cracks in steel beams are much more serious than cracks in concrete beams. However, the cracks in the FIU bridge where they can slide a folding rule in are alarming to me.
I have designed highway bridges for years before stepping into my current role of inspecting...
The diagrams are also typical for field work when parts have to be lifted or rigged for unloading. The workers measure the total piece length and then compute (using the ratios in the diagram) where to locate the slings. In these cases most folks don't care what the deflection is and that may...
I would think SC joints were common but not omnipresent. When designing joints that incorporate welding and bolting, SC bolts have to be used unless things have changed since I received my degree.
Hey folks,
I have a question from a supplier asking why we specify hot rolled steel sheet piling in accordance with ASTM A328 (or A572) but we do not mention cold formed sheet piling. Therefore our current specification prohibits cold formed steel sheet piling. It is my hope there may be an...
I appreciate the many cogent observations about the ridicules article. I hope you will enjoy my own humor ...
... then engineers should let others design the things that will harm people.
My particular favorite is the humor that anyone who doesn't appreciate what engineers are doing for them...
I can't help unless you give us an idea of the range of height you need to deal with. For example, if I were asked to design a RW that ranged from 10ft to 15ft, I may well just go with one design. If on the other hand I were asked to design a wall that ranged from 4ft to 32 ft, I would...
Colleagues,
I am a bridge designer so I deal with steel and concrete and big time loads so I just don't have a feel for typical residential wood design. I offered to help a buddy design or scope out what it would take to build a shed on his property. He has some grand ideas and I'm trying to...
Yes, minimal length bolts are often supplied fully threaded and they carry the designation indicated by ATSE, with the "-T" indicating fully threaded. Only short bolts ar emade this way typically when A325 or A490 are specified. If you need a special threaded length, you will probably need to...
If the environment were the cause for concern they would have us believe, they would insist that all countries adhere to the proposed policies and not just a handful of "developed" countries. Only the virtuous countries need to fear treaties like the Kyoto protocol since only they would attempt...
The 32 kips is an axle load, not a wheel load. The two wheels are spaced a little over 1800mm transverse. I believe there is also a "design tandem" that you should analyze too. This is four smaller wheel loads instead of two larger ones.
In my experience column reinforcement around the perimeter gets congested (when it must be spliced) at around 2%. Check the formulas for maximum top size of aggregate and some other bar spacing limits and you will see that it will be quite difficult to get anywhere near 8%.
I have not designed a concrete member in quite some time but I seemt to recall there was a maximum YP allowed for mild steel, which was something around 75ksi. Is this still in the code or has it really been that long?
hokie66,
Of course an architect designed it ... would an engineer?
It is a sci-fi dream to build something like that. The practical problems of excavation and shoring during construction will pursuade them to do something else.
Holding back the load after it is built shouldn't be a problem...
That's OK. I used 1.2 Hz for the calculations because it yielded the highest amplitude. This fits well with 1-1.5 since it is in the middle of the range. It is only a 1DOF undampened vibration model. There is no need to fine tune something with such limited response in the model.
But...