Maybe there is the method to recharge the battery - let's say the solar panel installed on the buoy anchored over this underwater system (wire connection probably is not to avoid however). It depends how deeply is to be sunken.
Probably there are lighting buoys with independent supplying...
Sspeare: "Electrician has now adjusted the instantaneous trip on both CBs to 7X the breaker rating. We will see what happens".
I am not sure if I understand you, however I can't abstain from the caution: it may be a mistake. To "see what happens" may be not proper strategy.
Look: 7x rating = 7...
Do you know now which breaker was tripping first?
I have no idea how to help you. CB#2 is crucial for the safety of your motor. CB#1 should trip later than CB#2, so the time setting here would have the desirable effect (if possible anyway to set anything on it).
In my opinion the...
Well, "MOTOR CIRCUIT PROTECTOR" sounds quite good, similarly as SOLID STATE SOFT-START CONTROLLER. If this MCP is equipped with real protection of the motor, I may withdraw some my previous claims and reservations referring to the CB #2 (after getting your scheme and parameters maybe I'll be...
Well, I am not sure if I understand your note. However as far as I can understand I just try to advice you in your 3 questions and others.
1) You have to know which CB tripped, it is absolutely necessary for going farther. I can't understand this electrician who don't know which one tripped...
No problem.
I found that in my text above the last-but-one sentence should be correctly in such a way: "In addition I stated the similar question referring to the 2-nd harmonic and I answered "yes".
A mistake may be a fatigue symptom.
Regards
CL
Gunnar: "The first three answers to the OP were very much tongue-in-cheek".
I can't agree with your opinion. My very first answer was absolutely serious.
Question was "yes or no?" and my answer was "no". In addition I stated the similar question referring to the 3-rd harmonic and I answered...
1. The magnetising current inrush in a transformer is "rich" in 3rd harmonic? yes or no?
NO
2. The magnetising current inrush in a transformer is "rich" in 2nd harmonic? yes or no?
YES
Do you think about geodesic measurements? I am not the surveyor, I can't help you.
You may try with the www: http://en.wikipedia.org/wiki/Surveying and other professional sites, companies or persons.
Regards
I thank everybody for your advice and information.
Rafiq, don't hesitate to talk about such things as I consider. I am an experienced designer and I won't do such mistakes as you mentioned.
I am in contact with people from the utility company and I know some data. I want to verify this...
If you suggest that 60-70 W/m2 is not bad I may say that I think just also about such a coefficient. Bluntly speaking I am afraid that I may make the mistake to undervalueting the toatal demanding power (the risk of the discredit).
Regards.
RBulsara,
thank you for your advice. Haven't you any own experience in this topic?
I have some data, of course. Designers are likely here to do prior estimation at the higher level than it is in the real life (similarly, some guides and publications). However this is not so stupid because the...
RBulsara,
well, you are absolutely right.
However please have a look at this case - you have cable-core-CSA=16mm2 and the current load 2*2A=4A in total.
Are you really likely to check dimensioning of this cable on the condition of the withstanding of the total load?
By the way, you should...
I would like to ask you about the real power consumption for the A-class office building.
The problem is that we designers have to prepare the application to the grid operator here in Warsaw, Poland, for technical conditions for supply for such a high-rise tower of about 70,000 sq. meters...
Are you asking for the formula for voltage drop?
deltaU% = 200 * l * L * cos? / (gamma * A * U) [%]
deltaU = 2 * l * L * cos? / (gamma * A ) [V]
You have
U=230V, I=4A, cos?=0,8 or 1,0 or something else (you probably know it)
L=800m, gamma =57 [m/Ohm*mm2] for Cu or 33 for Al
A=16mm2
For your...