  1. courtnvm

    Steel Stair Seismic Design

    I have posted a couple of threads regarding this subject in the past, but I would like to post a more thourough question regarding providing seismic design on steel stairs. I have a particular project which is in the Missouri area and is governed by the 2006 IBC and ASCE 7-05. I have about 6...
  2. courtnvm

    Glass Guardrail Deflection

    Does anyone have information regarding what is the allowable deflection of a cantilevered glass guardrail system which has 4-way spider fitting at each lower corner of panel analyzed as thin plates. The glass would be tempered glass. When I analyze the panel using thin plate theory, I get a...
  3. courtnvm

    Stair Stringer Connection to 6" Structural Slab

    Okay, I have a fun and interesting challenge. I am providing calculations on a stair that has the stair stringer attaching to a 6" structural concrete. The steel fabricator has fabricated and installed a mirrored image of this stair. They are proposing to connect the stringer to the 6" slab...
  4. courtnvm

    HSS Local Bending Check

    How did you check the yielding of the column face? I looked at the Blodgett Formula as discussed above and got an allowable force of 10.5 kips. I could be missing something though. The force is vertical. The HSS6x2 is LLV.
  5. courtnvm

    HSS Local Bending Check

    Yes, the 6x6 would work. The problem is that the fabricator took it upon himself to go ahead and fabricate and install the HSS6x2x1/4. What I am trying to say is that everything is installed and now I have to provide damage control.
  6. courtnvm

    HSS Local Bending Check

    I have a situation where a HSS6x2x1/4 horizontal outrigger is welded between a HSS12x2x1/4 stair stringer and a HSS6x6x3/8 building column. The HSS6x2x1/4 is welded all around at each end. I am very concerned about the connection of the HSS6x2x1/4 to the building column becuase of local...
  7. courtnvm

    Stacked HSS Columns at Steel Stair Tower

    Okay, I found the AISC specification regarding bearing joints for compression members. Spec section J1.4 states the following: "When columns bear on bearing plates or are finished to bear at splices, there shall be sufficient connectors to hold all parts securely in place. When compression...
  8. courtnvm

    Stacked HSS Columns at Steel Stair Tower

    jike, the landings are supported at three corners using stiffened angle seats welded to steel embed plates and the fourth corner has the stacked column. As of right now, the fabricator want to only weld the 2" side of the tube to the channel flange, which would only give me 3 inches of weld. I...
  9. courtnvm

    Stacked HSS Columns at Steel Stair Tower

    Well originally the columns were designed as continuous, but the contractor did not locate the stair tower walls correctly, therefore geometry concerns come into play. In order to get the correct stair widths to meet code egress requirements the columns had to be stacked. My original question...
  10. courtnvm

    Stacked HSS Columns at Steel Stair Tower

    I have a 6 story stair tower which has a stacked HSS column the whole height of tower. The columns are intersected by the landing members. In essence what I have is a HSS6x2x3/8 column and MC12x10.6 landing member. The HSS6x2 columns have end plates at each end and are welded off to the...
  11. courtnvm

    AISC 13th Edition and 2000 IBC

    Thank you for the replies. I went ahead and designed per the reference standards of the governing building code. Val
  12. courtnvm

    AISC 13th Edition and 2000 IBC

    If I am providing calculations on steel connections for a project governed by the 2000 IBC, is it acceptable to use the AISC 13th edition? I believe the AISC LRFD 3rd edition is referenced in the 2000 IBC. Val
  13. courtnvm

    Kinked Steel Stair Stringer

    I guess I didn't explain that this stringer is an HSS12x3. Val Courtney, PE Valstone Engineering, Inc.
  14. courtnvm

    Kinked Steel Stair Stringer

    I built a RISA model of the stringer with the CMU wall stiffness included. I believe the CMU wall will move enough locally (about 1/4") to relieve most of the thrust that was occuring. The thrust in the stringer is approximately 2 kips and I am comfortable with that.