Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by corrosivo

  1. corrosivo

    Help with H2S certification.

    jraef There is an interesting technical paper that describes what sjvanhecke described in his post. Mrs. Bella (the author) have worked in this area and maybe she can help You. I pasted the information below...
  2. corrosivo

    Functions of Regulators and Capacitor Banks

    Stonemug From your post, I understand that you have detected power frequency hum in the communication cables, maybe your shield is part of a ground loop of the power system ground; verify this. The site below, shows a good graphical description of some of the causes and solutions of your noise...
  3. corrosivo

    Help with H2S certification.

    jraef As you said this gas is corrosive, especially to the copper wires and bars. I recall working in a Hydroelectric plant that the air in the whole area smelled like rotten eggs due to decaying organic matter in the lake. After several years this gas was corroding everything made of copper...
  4. corrosivo

    Gas Groups for Flammable Gases and Vapours

    pristava Check with the chemical engineers site. Regards
  5. corrosivo

    3 phase power question

    Jpr2004 Please check thread237-102768. You cannot add currents arithmetically; your KWHR meter is telling you the truth, your A/C is consuming more power than the motors. There is an important reactive component in your input and output currents in your setup that do not contribute to the real...
  6. corrosivo

    Earthing of supervisory screen

    Flickstar By Grounding both ends of the shield you will have circulating currents in the signal wires, the reason is that the shield will be in parallel with the power ground that connects both equipments. When there is a flow of current in your shield you will have magnetic field right next to...
  7. corrosivo

    open source optimization programs

    dafo74 I agree with Mstrvb19, this is a complex issue. You need to use a computational model which includes all the hydro, thermal players such as generators, IPPs, transmission and distribution networks etc. which determines the optimal operation of your network (least cost), This can affect...
  8. corrosivo

    Differential Trip

    wr180561 I think you do not have a real fault in the windings, if that were the case you will have other symptoms on your machine. An internal fault in a generator rapidly becomes catastrophic. Looks that the relay tripping is dependent on the loading of the generator. Did the generator tripped...
  9. corrosivo

    Bearing Damage on VFD motor

    Everst You have a mechanical background, I do not know how familiar you might be with these solutions we are suggesting to you, but here are some additional comments. I agree with skogsgurra explanation, some type of insulation must be provided to the bearing (Ceramic, Insulated pedestal etc.)to...
  10. corrosivo

    Bearing Damage on VFD motor

    Everest I agree with DickDV; this type of arrangement have been used for decades in the gas and steam turbines multimegawatt generators. You need a grounding brush riding on the shaft to give the shaft induced voltages safe path to ground, what is happening is that an enough high potential...
  11. corrosivo

    exposed underground conduit

    axd38 Peebee is right but the job is already done, it looks that the manhole is at a higher level than the panel. I pressume that you cannot deenergize the panel for a long time. Your best bet in this case besides of installing a new conduit section (difficult & expensive but best solution), is...
  12. corrosivo

    cleaning motors in service

    yulinios In general there is no best way to clean a motor in service, and this action must be done as a last resource. Because you do not have full access to the windings with the motor end covers in place it will be very difficult to do a complete winding cleaning. What will happen is that the...
  13. corrosivo

    An unusuall case on Insulation Resistance Test on MI Cable

    EEAOC These readings are not unusual, they are telling you that the ph. A have very low insulation resistance to ground and the other ph. are ok. What are the readings between phases? You must look for the cause of this low reading, probably the cause of the low reading is in a very localized...
  14. corrosivo

    flexible wire for motors and starters

    kkgg Be careful with the extra flexible cable as the inner bunches of strands in this type of cable can slide out of the mechanical or compression type of connectors resulting in a loose connection later; when the bends (as in a tight enclosure) in the cables are too short radius or too near to...
  15. corrosivo

    when reversing a 3-phase motor

    durf208 Your question is not "dumb" is a perfectly valid question, you were told right, any 2 phases can be exchanged to reverse rotation in a 3 ph. motor, no harm will be done to it, but be careful because the load it drives might not tolerate reversal of rotation like a centrifugal compressor...