What is the condition of the terra cotta? Any cracks?
What is the age of the terra cotta?
How is the terra cotta connected to the backup masonry?
What is the condition of the anchors between the terra cotta and the backup masonry?
Where are the new anchors in relation to the terra cotta joints"...
In addition to what everyone else said, if the diagonal braces (and brace forces) are large compared to the floor beams, you might want to consider configuring the (large) diagonal brace as a single long member, and interrupting the (relatively wimpy) floor beams between the brace. For example...
I'll bet that six little kids (or two drunk teenagers) could really get that balcony bouncing. (I remember getting a pedestrian suspension bridge bouncing (with a few friends) when was 11-years-old, long before any of us knew the definition of "resonance".) I also noticed the balcony slightly...
These sheds are on just about every street in Midtown Manhattan. They appear to be almost semi-permanent. Some building owners even seem to be making money with them by selling advertising space on them - perhaps to offset the monthly rental cost. (I wonder how much they pay per month for these...
This (the rebar congestion at the column / roof slab joint) is not as bad as I thought. If you have an 8” flat plate roof slab sitting on a column, then the vertical bars exiting the top of the column (with hooks) can’t be larger than #5 bars – or else they won’t be able to develop within the...
Thank you for your responses KootK, HTURKAK, and Nick6781! In my opinion ACI 318-19 Chapter 15 does not explain the requirements for beam-to-column moment connections (and the required details) clearly enough to be of any use. I am still a bit confused. The fact that the hooks need to be...
Thank you HTURKAK for your response! I’ll get a copy of the latest ACI 352. I still don’t see how turning the hooks into the joint will mitigate cracks, unless the hooks are made longer. I always had the mindset that the sole purpose of hooked bars was to facilitate the development of bars in...
ACI 318-19 Section 15.3.3.2 requires column vertical bar hooks to be turned into the center of the column at the top of the column. In my opinion, turning the hooks inward into the column poses some problems, versus orienting them outward. The hooked bars would be easier to install if the hooks...
Thank you Agbsh. You confirmed my concern. Just to be safe I'm going to specify ASTM A615-22 and A706-24 so the additional ductility requirements are included.
canwesteng - Thank you for the response. The confusion I have is that two of the three ACI 318-19 tables that I referenced refer to ductility requirements for ASTM A706. The third table references ASTM A615 reinforcing steel. I am sensing that the purpose of these three tables is to point out...