Leak could be from the chiller tubes as well as any flanges or gaskets. The refrigerant is entrained in the the oil. To release it you need to pull a vacuum in the system you will see thee refrigerant boil off out of the oil
Forget about the handbooks, this gentleman is in above his head. His HR department has placed a mechanical engineer in a Stationary Engineer's position. You should inform them before someone get's hurt. Mechanical design and operations two totally different fields.
I agree with the above post from GRW, your technician is doing an excellent job for your Facility. He is not hiding anything but giving you a "snapshot" image of your systems at the time he made the readings. These are dynamic systems that open and close acccording to programmed parameters. They...
A suggestion-NYC code - fail safe system in the case of dampers applies to duct smoke - fire smoke dampers that on loss of pneumatic air or the fire panel sending shutdown signal the dampers will always fail to the closed position. For class "E" buildings (Hi-rise) and healthcare the dampers are...
Methinks a closer look at the code would be warranted and remember that the code was written for good reason by reasonably reasonable people. Take a look at the NYC high pressure boiler code and you will see that with an installed economiser will save you 10% by heating the makeup air to the...
TBP is on the money - amines when put into a boiler are the only chemicals that leave the boiler with the steam. They are specifically designed to do that and when they go around the system they change the PH back to a neutral (you are hoping for a 7.0 PH (not likely but close is good enough...
Don't go near aluminum as far as danger of fire is concerned. It was tried and pretty much shoved down our throats to save money. After some fatal fires it was finally banned. You will hear a lot about special wire nuts and connectors, I would not trust any Al setup.
Interesting thread. Concerning smoke, in hospitals NYC we are required to either connect generator to 30 % of the nameplate rating or 50% of connected load. If either is not the case we must connect to a load-bank annually in increments of 30,50,75 and 100% in order to prevent unburned fuel from...
In New York you are under a number of alphabet agencies, such as DOH NYS Department of Health and Joint Commission,along with NYFD, DEC,ECB,EPA,DOB. ect.
DOH requires 20 ach, but does not state that I can remember that you can have an "off" period. The only time I have seen that apply is when...
One place to start is to realize just how inefficient it is to produce compressed air. One seminar that I attended claimed that making compressed air for operating dampers and controls is about 10% efficient. Yes that means 90% inefficient. Having been involved with HVAC (mostly in healthcare)...