  1. ciy

    IEC v ANSI Low Voltage Circuit Breaker Short Circuit Ratings

    gardengnome747, Thanks for your information. Kiribanda and veritas, Thanks for your opinion. I agree to select by Ics. It's safer selection. However, have any guide or practice to highlight how to select CB according to Icu/Ics? Please advise, if any. Thanks again.
  2. ciy

    IEC v ANSI Low Voltage Circuit Breaker Short Circuit Ratings

    Dear All, There is a question I wonder to know how select the breaker. It assumed already have the calculated fault current by SKM. Which do I select the Icu or Ics accordingly? For example, the said calculated value is 42kA @480V InitSymRMS 3P. IEC breaker rating Icu/Ics = 50kA/38kA @500V...
  3. ciy

    Shunt Reactor

    Dear Bill, thanks for your clue, I think I figure out.
  4. ciy

    Shunt Reactor

    Hi everyone, there is a question need your help. 33kV underground XLPE cable, 2000mm2, the length are 20kM. If we need to consider reactive compensation, how to size/calculate the capacity of shunt reactor? Are there any textbook or standard we can refer? Thanks all.
  5. ciy

    Arc Flash Labels

    Usually, you need to develop two scenarios, one for Utility and the other one for Generator. Then find the worst case to print on label.
  6. ciy

    SKM Result - Negative Voltage Drop

    Maybe you in-service some capacitors in your system.
  7. ciy

    Harmonic current direction

    7anoter4 and electricpete, Thanks for your excellent opinion. I also think that triplen harmonic current flow under a loop condition. Again, please advise how to get the magnitude of neutral current under unbalance condition? Should include triplen harmonic and unbalance current? Regards,
  8. ciy

    Harmonic current direction

    Hi, I find an image in the website accidently about the harmonic issue. This image mark the direction of triple order harmonic. So, I curious and wonder to know their direction if lost the neutral line or add grounding wire. Please find the five(5) schematic as attached and advise these...
  9. ciy

    Connections between Ground wire and Neutral wire in 3 Ph 4W System

    FreddyNurk and Bill, thanks for your reply. Bill, thanks for your excellent explanation.
  10. ciy

    Connections between Ground wire and Neutral wire in 3 Ph 4W System

    Hi, In 3φ4W power system like 208/120V and 416/240V, G and N wire need to take care. There are 4 connection cases between G and N wire as attached. Please advise which one is practice connection and their pros and cons. Any guideline or article that I can refer to ? Thanks for your advice. Have...
  11. ciy

    UnderVoltage Relay (27) Shall be trip the CB or just alarm only?

    Dear davidbeach and krisys, Thanks your reply.
  12. ciy

    UnderVoltage Relay (27) Shall be trip the CB or just alarm only?

    Dear all, Thanks for your reply. Is there any guideline for reference? ciy
  13. ciy

    UnderVoltage Relay (27) Shall be trip the CB or just alarm only?

    Hi, Please advise when undervoltage Relay (27) Shall be trip the CB or just alarm only? What is need to concern? Is there any criteria for following? Thanks. ciy
  14. ciy

    Three-winding transformer damage curve

    Thanks for your reply from Evergreen1231 and cranky108. The tertiary winding is also Wye connection. I wonder which damage curve of winding should be concerned? Secondary winding? Tertiary winding?
  15. ciy

    Three-winding transformer damage curve

    Dear all, There is a three-winding transformer rated: 345/13.8/6.9 kV transformer; 92/54.5/37.5 MVA The impedance percentage of PS/PT/ST is 16/13/1.9%. Please advise how to draw its damage curve? What is the difference between the 2 winding and 3 winding transformer? Thanks for your help in...