UFT12, I don’t believe we are talking about protecting racks as SD2 stated “… I wish it had racks..” in his original post. Therefore I would think we are discussing it being considered piled storage.
In my previous post where I was referencing the possibility of utilizing Misc Storage criteria...
I have the 2013 Handbook at hand so that’s what I’m referencing for section numbers, etc.
It would seem that you are getting to your EH2 hazard classification by going to Chapter 15: Protection for Palletized, Solid-Piled, Bin Box, Shelf or Back to Back Shelf storage of Plastic and Rubber...
It is my understanding that baffles are not required. Logic being that with such close spacing if more than one sprinkler is being effected, that it is also going to basically be in the plume of the fire, and that it will therefore'overcome' the cold soldering effect. If it doesn't overcome the...
Have seen those 'pie pans' too Travis :). In fact you'll see them in Dublin (Ireland) airport - which is pretty embarrassing.
cdafd, no I wouldn't be calling those heat collectors. I'd consider those to be water shields. I was referring to the section in FM 2-0 that UFT12 referenced.
FM 2-0...
Dear Forum.
NFPA 20 2013 Section 11.2.2.3 thru 11.2.2.5 discusses and has equations for modifying engine horsepower for installations with temperatures and elevation. However, is there a way to know/calculate what impact that reduction of horsepower will have on pump flow/pressure?
Any insight...
While FM doesn't call them heat collectors, that's effectively what they are doing. You have the choice of installing such to form a solid continuous flat obstruction such that the heat will collect and the sprinkler activate or else space the sprinklers at 4' spacing under a non flat, non solid...
I think it might be a Multiple Jet Control Valve. Similar to one link this http://www.fireguard-uk.com/products/sprinkler_systems/multiple_jet_control_valve.htm
Would seem as long as the dog houses are heated then the feed main to the dog houses could be heat traced per NFPA 13 2013 8.16.4.1.3.
If the heat tracing is just protecting feed mains then my understanding is that the heat tracing just has to be approved. If the heat tracing is protecting...
FM 3-0 Section 3.2 still allows a C Factor of 120 for Galvanized while only allowing 100 for black steel.
FM 2-0 Section 2.5.2.5 also states where galvanized or stainless pipe must be used (black steel only allowed on dry pipe with inert gas btw).
FM have however done a very intensive technical...
cdafd (Specifier/Regulator)1 Feb 18 00:41
I don’t know.
If your lines are at say 20 feet and you pipe down for the valve,,
Will you really get air out??
Copied your response to the other thread here cdafd.
I would think you'd get air, then some spluttering, a somewhat steady stream of...
I could see some benefits to the manual configuration.
For the Automatic type they would have to be located at the high point which may be inaccessible for servicing in the future. Also, if you really wanted to get all (or at least most) of the air pockets out you'd end up with multiple Auto...
FM 2-1 (Prevention and Control of Internal Corrosion in Automatic Sprinkler Systems) Section 2.3.1 has 'recommendations' for new sprinkler systems that also mention Air Vents such as the datasheet cdafd linked to. However in FM 2-1 it looks for "... means for air release at the highest point of...