If you plan on learning centrifugal chiller service proceedures on the internet, do us one favour; Be totally upfront with the service mechanic when he is eventually called in to repair the original problem plus the additional problems created. Nothing is more frustrating than trying to...
I'm not sure that I've ever heard of studies being done on 'worn out' equipment.
Sounds like the compressors need an overhaul, stop trying to be a hero.
There are numerous manufacturers providing pipe sizing methods and proceedures. If you really have "no clue" you may wish to get help from someone with experience. A much cheaper alternative than compressor replacements, etc.
You design for a specific static pressure and select equipment appropriately OR roughly select your equipment and ensure the duct design is compatible. It really is just that easy.
Set up the system to use the electric reheat in conjunction with the mechanical cooling? An option if the increase in operating costs aren't prohibitive.
....snippage....
"How will this increased flow affect the operation of the compressors in a packaged air handler downstream?"
The condensing pressure will decrease, the condensor water side temperature rise will decrease, the approach temperature will increase and if the flow rate is...
If the existing system has an orifice for a metering device the low and high side pressures equalize during the off cycle. Most single phase compressors will not start or start properly against a pressure differential. This differential on start-up MAY be created with the addition of a liquid...
If you are convinced you need either of these options, choose the pump down control.
It is easier to install, involves no field basterdization of the outdoor unit and probably no brazing or the removal of the refrigerant charge to flare in a solenoid valve.
You will also need a pressure...