Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by Chapmeister

  1. Chapmeister

    Noisy Tranformer - Bad core laminations?

    That's a good idea. I'll discuss it with my superior. I'm going to recommend more testing (ensuring the leads are attached properly), and maybe an analysis of the motor control cabinet. Thanks again to everyone who offered info and advice. If I see any further conclusion to these issues I'll...
  2. Chapmeister

    Noisy Tranformer - Bad core laminations?

    OKAY, here's what the "technical representative" said in his reply: "Yes, it looks like the PT may have been reversed. Hard to say for sure, but it is either that or you have a more serious power problem that we first thought! <G>" I'm not sure what the "<G>" means.. but it looks like I might...
  3. Chapmeister

    Noisy Tranformer - Bad core laminations?

    Well the fact that the waveforms are not as expected, and the powerfactor is significantly lower than I think they should be, I'd say the leads were hooked up wrong. The thing is, I remember when he hooked them up, he said "the tester won't allow them to be backwards, it'll beep or something"...
  4. Chapmeister

    Noisy Tranformer - Bad core laminations?

    We have a piece of metering equipment installed in the switchgear which shows the instantaneous kVA, kVAr, kW, pf, etc. of the SG bus. It claims a pf of 0.77, which is okay. Why would the pf on the transformer primary be so bad (0.5pf)? I'm starting to get the feeling that the test equipment...
  5. Chapmeister

    Noisy Tranformer - Bad core laminations?

    I just collected the info off the DC motor: Brand: Thrige-Scott Ltd. Type: Shunt Motor Power: 150kW RPM: 2000 Armiture: 460V - 350A Exciter: 360V - 6.1/4.85A Again, the control cabinet also powers some small melt-pumps and heats. I checked the power factor stated by the switchgear and it said...
  6. Chapmeister

    Noisy Tranformer - Bad core laminations?

    I will contact the person that performed the testing and point out the waveform issues mentioned. I agree that the vector sum of the waves should be zero, and clearly this is not the case.
  7. Chapmeister

    Noisy Tranformer - Bad core laminations?

    Thanks for your input everyone! I'll try to collect a few more load specifications which might help us find a solution. The puzzling thing is that we have 8 other similar extruders, a few with dedicated 175kVA tranformers, and they don't seem to make nearly as much noise. Of course, those ones...
  8. Chapmeister

    Noisy Tranformer - Bad core laminations?

    The transformer is fed from a large piece of switchgear (in the same room). The fuses are Ferraz Shawmut A6D300R. And the switchgear is fed from a 5MVA (25kV/600V) transformer. I'm not sure what you mean by an upstream rectifier? There's nothing else inline with the tranformer.
  9. Chapmeister

    Noisy Tranformer - Bad core laminations?

    http://myweb.dal.ca/~mr663256/IPG_Xfmr/Xfmr_Graphics.html Here is a link to the data graphics. I welcome any and all interpretations.
  10. Chapmeister

    Noisy Tranformer - Bad core laminations?

    It was proposed by the company that did the testing that the source of the bad current harmonic distortion could be a result of bad iron core laminations. From the email I recieved: ------- It is possible that these harmonics are at least partly responsible for the noise level in the...
  11. Chapmeister

    Noisy Tranformer - Bad core laminations?

    The sound level isn't really variable. It's either on or off: loud or quiet. If's definitely more than a hum, like a loud buzzing. We have a larger 750kVA in the same electrical room which makes half the noise but runs way hotter. As for reactors or thyristors, my knowledge of the internals of...
  12. Chapmeister

    Noisy Tranformer - Bad core laminations?

    Hmm that's an interesting thought. We had some professional maintenance guys do a visual inspection when the plant was shut down last month. They said everything was tight (probably referring to the connections), but as you say, perhaps something is too tight!? I still think it must be...
  13. Chapmeister

    Noisy Tranformer - Bad core laminations?

    The testing was performed on the primary side only. It's not an autotransformer. It's a K-Factor 13 as described at http://www.marcustransformer.com/vw/fs/p017.htm The Marcus site claims its design is aimed at non-linear loads. And it's 'features' are listed as: § Specifically designed copper...
  14. Chapmeister

    Noisy Tranformer - Bad core laminations?

    The primary voltage readings stayed below 347V for the duration of the 24 hour test. At some points the voltage dipped to as low as 338V, but only for short time periods. The voltage %THD stayed between 1.0% and 1.7%. So I don't believe the voltage is the problem. The loading on the transformer...
  15. Chapmeister

    Noisy Tranformer - Bad core laminations?

    Hey all, I have a 300kVA Marcus brand transformer with an excessively high sound output. The sound output has been metered at ~85dB, which is well over the rated 65dB. The transformer was only purchased and install a little over 1 year ago. It was physically inspected and is clean as a whistle...